[RE-wrenches] The Demise of WEEB
Andrew Truitt
atruitt at gmail.com
Mon Sep 13 22:31:50 PDT 2010
2 points:
1) For the sake of clarity: there are WEEB
LUGS<http://www.we-llc.com/Datasheets/204-0404-000003.pdf>and WEEB
CLIPS <http://www.we-llc.com/Datasheets/204-0404-000007.pdf>. WEEB Lugs are
comprised of very robust tin-plated copper lugs, stainless steel hardware,
and the actual WEEB, which is the stainless steel nippled "washer" that
pierces aluminum anodization. WEEB Clips are simply stainless steal nippled
washers that are installed between module and rail that form a bond,
theoretically eliminating the need to bond the module to a ground wire, so
long as the rails are properly grounded.
2) My biggest concern with the WEEB Clip is that the moment a top-clamp is
loosened the module is no longer grounded!!! To me that is not a good
grounding method. Mr Wiley is obviously a talented inventor and he makes a
strong argument for the quality of the bond that the WEEB Clip provides when
the clip is installed properly and all mounting hardware is properly
torqued. What I don't understand is the argument that this is as safe of a
product as a properly installed outdoor rated lug for the service tech who
has to work on that array.
A tin-plated copper lug with a stainless steel set screw will last. A
service tech working on a faulted array that was grounded with WEEB Clips
might not.
Andrew Truitt
Free agent
Golden, CO.
On Mon, Sep 13, 2010 at 10:04 PM, benn kilburn <benn at daystarsolar.ca> wrote:
> Hopefully any crew installing PV, and familiar with this debate (which
> they should be) can easily distinguish between the GBL-4 and the GBL-4DBT.
> The weight difference is quite noticeable. If it feels light for its size,
> it's aluminum, dont use it!!! If it has some distinct weight to it, then
> it's most likely the copper DBT, giv'er!
>
> So what other non-conductive materials are out there that could help
> resolve this frame bonding issue?
> Sunteck's BIPV SolarBlend module uses a polycarbonate frame which
> requires no bonding. Do any of you have any experiences with these? How
> were they to handle, install? Do they offer any hope or support for
> non-metallic module frames?
>
> benn
> DayStar Renewable Energy Inc.
> benn at daystarsolar.ca
> 780-906-7807
> HAVE A SUNNY DAY
> ------------------------------
> From: ray at solarray.com
> Date: Mon, 13 Sep 2010 11:14:36 -0600
> To: re-wrenches at lists.re-wrenches.org
>
> Subject: Re: [RE-wrenches] The Demise of WEEB
>
> I didn't do the original install, and I couldn't ID the lug because of the
> corrosion.
> I believe everyone is correct that this isn't the DBT rated lug, though.
> Another reason to use the WEEB: a crew can't accidentally install the
> wrong (but almost identical, when new) lug.
> I'm sure the non-DBT lugs got mixed together in a bin at some point.
>
> R. Walters
> ray at solarray.com
> Solar Engineer
>
>
>
>
> On Sep 12, 2010, at 5:41 PM, Jamie Johnson wrote:
>
> That looks like a tin plated aluminum lug (aluminum corrosion) with a
> plated steel screw (rusted screw).......
>
> Here is an explanation of the differences between both ILSCO GBL 4 lugs
> from John Wiles Code Corner in Homepower issue 102
>
> "The Ilsco GBL-4DBT is a lay-in lug
> made of solid copper, which is then tin-plated. It has a
> stainless steel screw to hold the wire. The lug accepts a #14
> (2 mm2) to #4 (21 mm2) copper conductor. It is listed for
> direct burial (DB) and outdoor use and can be attached to
> aluminum structures (the tin plate). The much cheaper Ilsco
> GBL-4 lug looks identical, but is tin-plated aluminum, has
> a plated screw, and is not listed for outdoor use."
>
> Jamie Johnson
> NABCEP Certified Solar PV Installer #031310-118
> General Manager
> SOLAR POWER ELECTRIC
> EC13001765
>
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] The Demise of WEEB
> From: "Peter Parrish" <peter.parrish at calsolareng.com>
> Date: Sun, September 12, 2010 6:50 pm
> To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
>
> Are you sure that's a ILSCO GBL-4DBT lug? I am pretty sure the set screw is
> not SS, which it should be to be the genuine part.
>
> - Peter
>
>
> Peter T. Parrish, Ph.D., President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com
> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
>
>
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
> On Behalf Of R Ray
> Walters
> Sent: Sunday, September 12, 2010 3:10 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] The Demise of WEEB
>
> A picture is worth a thousand words, (hopefully this will upload)
> Here's a traditional Ilsco Lug after less than 5 years near the ocean:
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
> <bottom.letterhead>_______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________ List sponsored by Home
> Power magazine List Address: RE-wrenches at lists.re-wrenches.org Options &
> settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List
> rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant
> bios: www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
--
"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!"
~William McDonough
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100914/0bad9cf0/attachment-0003.html>
More information about the RE-wrenches
mailing list