[RE-wrenches] Enphase System Labeling

Dana Orzel dana at solarwork.com
Thu May 20 08:30:47 PDT 2010


This is per our AHJ.

 

Thanks,

 

Dana Orzel

Great Solar works, Inc.

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.414

C - 970.209.4076

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Wednesday, May 19, 2010 3:21 PM
To: Wrenches
Subject: Re: [RE-wrenches] Enphase System Labeling

 

Thanks for sharing that Dana,

 

Are you required by code or the AHJ, for micro-inverter systems, to have an
additional AC d/c aside from the branch circuit breaker? (on the roof or
other location)

 

For these micro-inverter systems the only labeling required here, by code
(CEC), is;

84-030 (1) which states...   

" A warning notice of an interconnected system shall be installed in a
conspicuous place at the supply authority disconnecting means of Rule 84-022
and the supply authority meter location."

 

84-022 is generally referring to the load center main breaker.  And the
utility company puts their own "WARNING: interconnected system" label at the
meter.

 

So we don't 'have to' provide any additional info, but i think that
providing some is a good idea. As Ray pointed out, too much info can be
discouraging.

 

For now, I have opted for these labels on the load center as the only
labeling for the system;

Code required -- "WARNING Two Power Source Parallel System" and;

Optional for info -- "Grid-Connected Solar Electric System

                                    Array Rating: 660 WDC

                                Module Rating (each): 220 WDC"

....the optional one will of course need to be replaced and updated if/when
the owner decides to add to his system.

 

cheers,

benn


DayStar Renewable Energy Inc. 

benn at daystarsolar.ca

780-906-7807 

HAVE A SUNNY DAY 

 

 

  _____  

From: dana at solarwork.com
To: re-wrenches at lists.re-wrenches.org
Date: Mon, 17 May 2010 14:29:12 -0600
Subject: [RE-wrenches] Enphase System Labeling

This was our last batch

 

 

 

          Labeling For Grid-tie Solar Electric System

Great Solar Works, Inc., 970-626-5253

 

                                                                KNOPP SIGNS


 

Qty - 2, Color red

 

INTERACTIVE SYSTEM POINT OF INTERCONNECTION

Enphase Micro-Inverters [1] per module [17] Total

 

PHOTOVOLTAIC SYSTEM SOURCE

 

                  PV System Total Watts
3.910   KW

                  Maximum AC Output Operating Current             13.6
Amps

                  AC Operating Voltage
240      Volts  

                  

For information and service contact: 

Great Solar Works, Inc., 970-626-5253

 

Qty - 1, Color red

 

PHOTOVOLTAIC SYSTEM SOURCE

 

                  PV System Total Watts
3.910   KW

                  Maximum AC Output Operating Current             13.6
Amps

                  AC Operating Voltage
240      Volts  

                  

For information and service contact: 

Great Solar Works, Inc., 970-626-5253

 

Qty - 1, Color red

 

PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT

WARNING - ELECTRIC SHOCK HAZARD - DONOT TOUCH TERMINALS.

TERMINALS ON BOTH THE LINE AND LOAD SIDES MAY BE ENERGIZED

IN THE OPEN POSITION. IF A GROUND FAULT IS INDICATED THE NORMALLY GROUNDED
CONDUCTORS MAY BE ENERGIZED AND UNGROUNDED

 

For information and service contact: 

Great Solar Works, Inc., 970-626-5253

 

Qty -1, Color Yellow

 

PHOTOVOLTAIC SYSTEM CONNECTED

THE AC PV DISCONNECT IS LOCATED 

Next to Meter on South Wall 

For information and service contact: 

Great Solar Works, Inc., 970-626-5253

 

 

 

Thanks,  Dana Orzel

 

Great Solar Works, Inc

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

Responsible Technologies for Responsible People since 1988"

 

 

  _____  

30 days of prizes: Hotmail makes your day easier! Enter now
<http://go.microsoft.com/?linkid=9729704> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100520/91ef1404/attachment-0003.html>


More information about the RE-wrenches mailing list