[RE-wrenches] Enphase System Labeling
benn kilburn
benn at daystarsolar.ca
Wed May 19 14:21:26 PDT 2010
Thanks for sharing that Dana,
Are you required by code or the AHJ, for micro-inverter systems, to have an additional AC d/c aside from the branch circuit breaker? (on the roof or other location)
For these micro-inverter systems the only labeling required here, by code (CEC), is;84-030 (1) which states... “ A warning notice of an interconnected system shall be installed in a conspicuous place at the supply authority disconnecting means of Rule 84-022 and the supply authority meter location.”
84-022 is generally referring to the load center main breaker. And the utility company puts their own "WARNING: interconnected system" label at the meter.
So we don't 'have to' provide any additional info, but i think that providing some is a good idea. As Ray pointed out, too much info can be discouraging. For now, I have opted for these labels on the load center as the only labeling for the system;Code required -- "WARNING Two Power Source Parallel System" and;Optional for info -- "Grid-Connected Solar Electric System Array Rating: 660 WDC Module Rating (each): 220 WDC"....the optional one will of course need to be replaced and updated if/when the owner decides to add to his system.
cheers,benn
DayStar Renewable Energy Inc. benn at daystarsolar.ca780-906-7807 HAVE A SUNNY DAY
From: dana at solarwork.com
To: re-wrenches at lists.re-wrenches.org
Date: Mon, 17 May 2010 14:29:12 -0600
Subject: [RE-wrenches] Enphase System Labeling
This was our last batch
Labeling For
Grid-tie Solar Electric System
Great Solar Works, Inc., 970-626-5253
KNOPP SIGNS
Qty – 2, Color
red
INTERACTIVE SYSTEM
POINT OF INTERCONNECTION
Enphase
Micro-Inverters [1] per module [17] Total
PHOTOVOLTAIC SYSTEM
SOURCE
PV
System Total
Watts
3.910
KW
Maximum
AC Output Operating Current 13.6
Amps
AC
Operating Voltage 240
Volts
For information and
service contact:
Great Solar Works, Inc.,
970-626-5253
Qty – 1, Color
red
PHOTOVOLTAIC SYSTEM
SOURCE
PV
System Total
Watts
3.910
KW
Maximum
AC Output Operating Current 13.6
Amps
AC
Operating Voltage 240
Volts
For information and
service contact:
Great Solar Works,
Inc., 970-626-5253
Qty – 1, Color
red
PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT
WARNING - ELECTRIC
SHOCK HAZARD - DONOT TOUCH TERMINALS.
TERMINALS ON BOTH THE
LINE AND LOAD SIDES MAY BE ENERGIZED
IN THE OPEN POSITION.
IF A GROUND FAULT IS INDICATED THE NORMALLY GROUNDED CONDUCTORS MAY BE
ENERGIZED AND UNGROUNDED
For information and
service contact:
Great Solar Works,
Inc., 970-626-5253
Qty -1, Color Yellow
PHOTOVOLTAIC SYSTEM
CONNECTED
THE AC PV DISCONNECT
IS LOCATED
Next to Meter on
South Wall
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Thanks,
Dana Orzel
Great
Solar Works, Inc
E -
dana at solarwork.com
V -
970.626.5253
F -
970.626.4140
C -
970.209.4076
web
- www.solarwork.com
Responsible
Technologies for Responsible People since 1988"
_________________________________________________________________
30 days of prizes to be won with Hotmail. Enter Here.
http://go.microsoft.com/?linkid=9729709
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100519/00427959/attachment-0003.html>
More information about the RE-wrenches
mailing list