[RE-wrenches] Enphase System Labeling

benn kilburn benn at daystarsolar.ca
Wed May 19 14:21:26 PDT 2010


Thanks for sharing that Dana,
Are you required by code or the AHJ, for micro-inverter systems, to have an additional AC d/c aside from the branch circuit breaker? (on the roof or other location)
For these micro-inverter systems the only labeling required here, by code (CEC), is;84-030 (1) which states...   “ A warning notice of an interconnected system shall be installed in a conspicuous place at the supply authority disconnecting means of Rule 84-022 and the supply authority meter location.”
84-022 is generally referring to the load center main breaker.  And the utility company puts their own "WARNING: interconnected system" label at the meter.
So we don't 'have to' provide any additional info, but i think that providing some is a good idea. As Ray pointed out, too much info can be discouraging. For now, I have opted for these labels on the load center as the only labeling for the system;Code required -- "WARNING Two Power Source Parallel System" and;Optional for info -- "Grid-Connected Solar Electric System	                          Array Rating: 660 WDC	                      Module Rating (each): 220 WDC"....the optional one will of course need to be replaced and updated if/when the owner decides to add to his system.
cheers,benn
DayStar Renewable Energy Inc. benn at daystarsolar.ca780-906-7807 HAVE A SUNNY DAY





From: dana at solarwork.com
To: re-wrenches at lists.re-wrenches.org
Date: Mon, 17 May 2010 14:29:12 -0600
Subject: [RE-wrenches] Enphase System Labeling
















This was our last batch

 

 

 

          Labeling For
Grid-tie Solar Electric System

Great Solar Works, Inc., 970-626-5253

 

                                                               
KNOPP SIGNS       

 

Qty – 2, Color
red

 

INTERACTIVE SYSTEM
POINT OF INTERCONNECTION

Enphase
Micro-Inverters [1] per module [17] Total

 

PHOTOVOLTAIC SYSTEM
SOURCE

 

                  PV
System Total
Watts                     
                      3.910
  KW

                  Maximum
AC Output Operating Current              13.6
    Amps

                  AC
Operating Voltage                                              240
     Volts  

                  

For information and
service contact: 

Great Solar Works, Inc.,
970-626-5253

 

Qty – 1, Color
red

 

PHOTOVOLTAIC SYSTEM
SOURCE

 

                  PV
System Total
Watts                     
                      3.910
  KW

                  Maximum
AC Output Operating Current              13.6
    Amps

                  AC
Operating Voltage                                              240
     Volts  

                  

For information and
service contact: 

Great Solar Works,
Inc., 970-626-5253

 

Qty – 1, Color
red

 

PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT

WARNING - ELECTRIC
SHOCK HAZARD - DONOT TOUCH TERMINALS.

TERMINALS ON BOTH THE
LINE AND LOAD SIDES MAY BE ENERGIZED

IN THE OPEN POSITION.
IF A GROUND FAULT IS INDICATED THE NORMALLY GROUNDED CONDUCTORS MAY BE
ENERGIZED AND UNGROUNDED

 

For information and
service contact: 

Great Solar Works,
Inc., 970-626-5253

 

Qty -1, Color Yellow

 

PHOTOVOLTAIC SYSTEM
CONNECTED

THE AC PV DISCONNECT
IS LOCATED 

Next to Meter on
South Wall 

For information and service contact: 

Great Solar Works, Inc., 970-626-5253

 

 

 



Thanks, 
Dana Orzel

 

Great
Solar Works, Inc

E -
dana at solarwork.com

V -
970.626.5253

F -
970.626.4140

C -
970.209.4076

web
- www.solarwork.com

Responsible
Technologies for Responsible People since 1988"



 






 		 	   		  
_________________________________________________________________
30 days of prizes to be won with Hotmail.  Enter Here.
http://go.microsoft.com/?linkid=9729709
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100519/00427959/attachment-0003.html>


More information about the RE-wrenches mailing list