Will non-linear loads be expected?  If so, the neutral is considered to be 
a current carrying conductor and needs to be counted.  If no non-linear 
loads, then the neutral is not counted.

Code citation below (2008):

310.15(4) Neutral Conductor.
(c) On a 4-wire, 3-phase wye circuit where the major
portion of the load consists of nonlinear loads, harmonic currents
are present in the neutral conductor; the neutral conductor
shall therefore be considered a current-carrying conductor.