<font size=3>Marco:<br><br>
Will non-linear loads be expected?  If so, the neutral is considered
to be a current carrying conductor and needs to be counted.  If no
non-linear loads, then the neutral is not counted.<br><br>
Code citation below (2008):<br><br>
<i>310.15(4) Neutral Conductor.<br>
(c) On a 4-wire, 3-phase wye circuit where the major<br>
portion of the load consists of nonlinear loads, harmonic currents<br>
are present in the neutral conductor; the neutral conductor<br>
shall therefore be considered a current-carrying conductor.<br><br>
<br>
</i>William Miller<br><br>
PS:  Who's buying dinner, you or your partner?<br><br>
Wm<br><br>
<br><br>
At 09:17 PM 5/13/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Content-Type:
multipart/alternative;<br>
<x-tab>        </x-tab>boundary="----=_NextPart_000_02F9_01CAF2C8.8607F590"<br>
Content-Language: en-us<br><br>
xmlns:ns0="urn:schemas-microsoft-com:office:smarttags">
<br>
Thanks for sending that link, William.<br>
 <br>
OK…let’s try it from a different perspective.<br>
 <br>
When you’re running, say, three three-phase hot conductors from point A
to point B with a neutral conductor, should that neutral be considered
“current carrying” from the perspective of more than three “current
carrying” conductors in a raceway?  And thereby necessitating
de-rating the current carrying capacity of the hot conductors?<br>