William Miller william at millersolar.com
Mon Jan 11 17:39:05 PST 2010


Kirpal:

Can't you disconnect the load at the inverter and then go back to the array 
to disconnect the feeder?

William

At 04:01 PM 1/11/2010, you wrote:
>William.....we love the Outback FWPV12 and 8.......a good improvement
>over the PSPV......we use them high voltage apps, but alas......don't
>open fuse under load.....thats why we need a version which is
>disconnectable......
>Cheers,
>
>--
>Sunny Regards,
>Kirpal Khalsa
>NABCEP Certified Solar PV Installer
>Renewable Energy Systems
>www.oregonsolarworks.com
>541-218-0201 m
>541-592-3958 o
>
>
>On Mon, Jan 11, 2010 at 12:16 PM, William Miller
><william at millersolar.com> wrote:
> > Kirpa:
> >
> > Have you considered using the Outback PSPV combiner with the 600 VDC
> > touch-safe fuse holders and appropriate fuses?  I belive this configuration
> > meets the 600 VDC rating.
> >
> > William Miller
> >
> >
> >