On 8/1/09 11:08 , William Miller wrote:
> Our best solution would be to install a 200 amp meter panel with a 100
> amp breaker. The application is an agricultural based residence, so
> based on how one interpreted this, the back feed allowance would be
> either 100 amps or 120 amps, enough to cover our back feed.
>
> We were told by a supplier that we could purchase a 200 amp m/m/c and
> field retrofit a 100 amp breaker into it. We requested the supplier
> contact the manufacturer (GE) and obtain confirmation of this claim.
> We were assured that this was possible.
>
> Based on the assurances, we bid the job and won the contract. When we
> purchased the equipment we found that the 100 amp breaker could not
> physically fit into the 200 amp m/m/c. We spent a full day calling GE
> and then other manufacturers only to find out that no one builds a 200
> amp m/m/c that can fit a 100 amp main. All of the panels we looked at
> were cleverly configured to not allow the smaller breaker to be held
> in place.
>
> Has anyone out there found a 200 amp m/m/c that can fit a 100 amp
> main? If so, I want to know.
Not yet, and I would also be quite interested as we have a green
subdivision project in the wings which could use them.
I ran into a similar situation last year replacing an old 100A Zinsco
panel. I selected a 150A Siemens (which is really a relabeled 200A
unit) for its 24 breaker spaces, leaving room for PV tie-in plus main
panel surge suppression plus a little room for future expansion. The
utility was willing to allow a 125A service using the existing feeders,
but refused to do 150A ("that's not a standard size for us") without
upgrading quite a bit of overhead feeder. We bought the 125A main kit
for the same series of panel, only to find out what you did - that it
does not mount in the 150A or 200A versions of the panel. Because the
customer has a pending underground service (future residence, which will
supply the existing dwelling as a subpanel) they eventually agreed on a
backfed Q2100H (even more expensive) for the interim overhead service.
This was a separate meter application, not an all-in-one.