[RE-wrenches] FW: Backup Generators
    Mark Dickson 
    mark at OasisMontana.com
       
    Thu Jul 16 08:27:52 PDT 2009
    
    
  
Allan, 
I have two different systems using these EU6500 generators but instead of
the Trace they have a Magnum MS 4024 and 4024AE.  Both work flawlessly as
long as the eco-throttle is off.
 
Good luck!
 
Mark Dickson
Oasis Montana Inc.
 
  _____  
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Randy Brooks
Sent: Wednesday, July 15, 2009 7:40 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] FW: Backup Generators
 
Allan,
 
Does the Honda have a "eco-throttle" setting that throttles back under light
load?  If so, turn it off so the inverter sees full voltage and frequency
and can sync with no other loads on.
 
Randy Brooks
Brooks Solar, Inc.
Solar Power for People
140 Columbia View
Chelan, WA  98816
509-682-9646
Randy at BrooksSolar.com
www.BrooksSolar.com
 
On Jul 14, 2009, at 11:24 PM, Allan Sindelar wrote:
Wrenches,
This man wrote me about a generator/inverter compatibility problem he's
having. I haven't heard of it before. I suspect it's more than just a simple
voltage-frequency issue, but I haven't heard of this or experienced it. Any
ideas?
Thank you, Allan Sindelar
 
In the Spring of 08, I purchased a Honda EU6500is generator as a back-up to
my off grid solar system.  The Honda was to replace my Yamaha YG6600DE
generator which worked fine with my Trace SW4024 inverter.  However the new
Honda inverter-generator seemed to have problems working with my Trace
inverter.  If I had a load running, such as my 110 V well pump, it would
handle that load and the excess power from the generator was used to charge
the batteries through the Trace 4024.  But once the well pump shut off, the
Honda generator and the Trace didn't seem to like to work together.  The
Trace inverter stopped allowing the incoming power to be used to continue to
charge the batteries by disconnecting AC2 power (generator) from coming into
the SW4024.  After replacing the Honda with the old Yamaha generator,
everything worked fine again, including charging the batteries without
another load on the inverter.
As a result of the above, my question is:  Have you experienced similar
incompatibility with inverter-generators and inverters such as my Trace
SW4024?    If so, do you have any suggestions that will allow me to use my
Honda EU6500is with my Trace 4024?  Calls to Xantrex and Honda on this issue
did not provide any useful information.
Thank you, Michael 
 
_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090716/60b4ee9f/attachment-0004.html>
    
    
More information about the RE-wrenches
mailing list