[RE-wrenches] stacking grid tied Outback
Darryl Thayer
daryl_solar at yahoo.com
Fri Jun 26 06:25:07 PDT 2009
All inverters can be paralled on the output side, AC side no problem, it is the inputs that you can not Parallel--This will distroy the inverter
DT
--- On Fri, 6/26/09, Randy Hatch <randy at third-sun.com> wrote:
> From: Randy Hatch <randy at third-sun.com>
> Subject: Re: [RE-wrenches] stacking grid tied Outback
> To: jryago at netscape.com, "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
> Date: Friday, June 26, 2009, 7:20 AM
> Jeff,
>
> Could you expand on this comment, please:
>
> "We parallel Fronius inverters all the time with no problem
> as long as wire
> runs are short."
>
> Perhaps I am confused. How do you "parallel" the
> inverters?
>
> Does the method satisfy 690.64 (B)(1) requirements for
> Dedicated Overcurrent
> and Disconnect?
>
> I am using NEC 2008. Thanks for clarification.
>
> Thank you,
>
> Randy Hatch
> NABCEP #091308-28
> randy at third-sun.com
> www.third-sun.com
> p740-597-3111 x28, f740-597-9775
>
> Clean Energy - Expertly Installed
> Please consider the environment before printing this
> e-mail.
>
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
>
> [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> On Behalf Of Jeff Yago
> Sent: Thursday, June 25, 2009 4:57 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] stacking grid tied Outback
>
>
> Got a call to check out an existing, but distant system
> that a elderly
> couple spent over $200K for a pv/battery/wind system and
> system never worked
> right. Local electrician called to advise many design
> and wiring problems
> and suspects orignial installer had no clue.
>
> I have not seen the system yet, but was told he has ten
> (10) Outback
> inverters, 2 configured for sell back and 8 not. He
> said they called
> Outback and received 2 differnet recommendations concerning
> conversion of
> remaining 8 inverters to grid tie. Was told they
> could be factory
> re-configured to all sell back, but can only stack two
> inverters in sell
> mode.
>
> If true, why can't you just parallel multiple stacks of
> dual inverters and
> just feed each pair to their own circuit breaker in the
> main panel? We
> parallel Fronius inverters all the time with no problem as
> long as wire runs
> are short.
>
> Bottom line - note sure what we will suggest until I check
> it out tomorrow,
> but wanted to be able to advise which answer they received
> from Outback was
> correct.
>
> Thanks,
>
> Jeff Yago
>
> _____________________________________________________________
> Netscape. Just the Net You Need.
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-wrenches
mailing list