[RE-wrenches] Magnum MS4448AE Compatibility Question
Starlight Solar
larry at starlightsolar.com
Fri Feb 13 13:33:28 PST 2009
Allan,
I have a recent power issue come up with a Magnum inverter. A customer
tried to operate her Splindide washer/dryer but the motor would not
start. I looked at the waveform with a scope and RMS voltage and
frequency were fine. The waveform looked good until the motor tried to
start. The washer was putting a jagged noise riding on the sine wave.
The voltage and waveform still looked OK other than the noise. Mostly
sure that this was the cause, I grabbed a 600 watt cheap import sine
wave inverter and connected the washer. Same ripple was present on the
waveform but the $400 inverter would run the washer motor fine. It
also ran fine with a 1600 watt Honda inverter/generator. I have
written to Magnum about this and had no response to date (about 4 days
now).
Have you looked at the waveform while operating the igniter? Perhaps
this is a similar problem.
Kindest Regards,
Larry Crutcher
Starlight Solar
(928) 941-1660
Renewable Energy Products, Service and Installation
Mailing Address (NO SHIPPING):
Box 11114
11279 S. Glenwood Ave
Yuma, AZ 85367
Shipping and retail store (NO MAIL):
2998 Shari Ave
Yuma, AZ 85365
On Feb 9, 2009, at 11:16 AM, Allan Sindelar wrote:
> Wrenches,
> We have an unusual problem, and I need to know if anyone else has
> had this or a related problem, and what to do about it.
>
> This concerns a new off-grid residential system, very conventional:
> 1,800W PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16
> S-460s, installed summer 2008. This existing home is being
> extensively remodeled, and the home is not yet occupied. A local
> mechanical contractor installed a new infloor radiant (gypcrete)
> hydronic heating system using a Netherlands-made (German company)
> Buderus GB142 high-efficiency boiler. The problem is that the boiler
> won't start reliably on the inverter. It appears that the hot-
> surface igniter does not get full AC voltage (it runs on straight
> 120V AC, but is supplied through the boiler's control circuitry). We
> tested the igniter by disconnecting it and plugging it straight into
> inverter AC and it lit right up.
>
> The mechanical contractor has tried a replacement Buderus GB142
> boiler with the same result. I was told that they brought out a
> generator and it also failed to ignite on generator AC, but not
> knowing the generator used or the way it was wired (I believe an
> extension cord to a portable) I don't put much weight on this data.
> They also took a Lochinvar Boiler to the site to test the theory
> that a different manufacturer's boiler might work. The Lochinvar
> boiler, which uses a different control and a spark ignition rather
> than a hot surface igniter, worked on site without any problems.
>
> I'm looking for solutions. Magnum tech support had not heard of
> this. Have you?
> Also, if indeed we have an inverter that is incapable of running
> this load, how do we make it right to the homeowner and the
> mechanical contractor? What should be Magnum's obligation? What
> should be ours? This issue hasn't come up here since the days when
> the Trace SW mod-sine series was the waveform standard.
>
> Thanks,
> Allan Sindelar