Dave,
As you've seen on our installs we always use one or more strain
reliefs in the south end of the box. Including for the grounding
conductor. We use the nylon ones from Sealcon. There is no way that
the foam block and lid provide adequate strain relief.
http://www.sealconusa.com/productselection-ny.htm
Scott.
Scott M. Knapp, Ph.D.
Solartek LLC
Phone: 407-462-1182
Email: scott at solartek.com
Web: www.solartek.com
On Tue, Nov 24, 2009 at 3:12 PM, Dave Click <daveclick at fsec.ucf.edu>
wrote:
> Wrenches-
>
> How are folks wiring the Soladeck boxes? It seems that the intent is
> to use
> cord grips in the south end of the box, but I just saw another
> installation
> where the wires just came directly in through the space at the south
> end.
> Seems like the foam is included to keep bugs out rather than provide
> strain
> relief to those incoming conductors, so I guess I'm just looking for a
> reality check here.
>
> Thanks and happy Thanksgiving!
> DKC