[RE-wrenches] "its a UL listed assembly"

Nick Vida nickvida at ymail.com
Sun Nov 22 19:07:10 PST 2009


Thanks for a great response Matt, and an interesting lead to a product solution...

Let me preface this with saying I am installing another company's design, so all you are saying about proper
 gear at the service is totally heard, and this tap would not be something I would design...

The situation is a Wadsworth tandem 100amp main. Really rare and weird panel from the early 60s. It has
 2 service entrance masts, and a 8 jaw meter socket feeding 2 separate fused  100 amp load centers.

The design was to tap into one of these with 40amp fused disconnect from a sma 7000.

Unfortunately the wires in the Wadsworth gear is type TW which is not included in the Feeder exception of
 310.16. When this was discussed. I threw out there the idea of changing the wires. These guys wanted to
 void the listing for piercing taps and any other taps 

The REAL problem is the wording of NEC 690.64(B) because all these guys that are not willing to wrap
 their head around what the signal path/ back feeding/ over-current/ 230 tapping scenarios are... read 120
 and wants to apply it to everything in the system. These inspectors were explaining to me that the feeder IS
 the buss and 120%... and its really hard to explain the intent with the language of the paragraph. It needs to
 be 2 separately described scenarios in my opinion, to avoid the constant misunderstanding.

Also, the NEC says in 690.64 and the 230 reference there, that taps are permitted for solar... not much
 detail, not much help. 

It seems like these inspectors consider the "voiding the UL listing" is a dead wall conversation ender. I'm
 almost willing to admit you are right, it is totally valid, which makes the point of .64 come into question.

I hope you are right about newer gear having listed tapping means and large buses for solar. It seems like
 that will take a while to filter down because so many people work with electricians different than the solar
 installers they are working with (and because so many installers focus on solar and don't wire houses). I
 think the glimmer of hope that a tap will pass on a retrofit is gonna keep them around for some time. And I
 really think that the code needs to address the options better.