Hey Guys....Unirac recently changed their requirement to 2 clips between
each module.......one on the upper rail and one on the lower
rail......therefore by my count you need 2N-2 clips for N modules, you don't
need any clips at the ends of the row of modules........   the link to their
diagram and instructions is:  http://www.unirac.com/pdf/ii225_5.pdf


I think the overall intention is that it is better to not skimp on
grounding.....for all the inner modules in a row they are bonded to the
rails at 4 points, each of the rails has a ground lug.  Should any module be
removed for any reason the remainder of the modules are still solidly
grounded......

My understanding is that Uniracs ground lugs and clips are licensed from
Wiley so I would guess that the Wiley direct ground lugs and clips have the
same requirements......

My take is that this grounding system is soooooo much more convenient and
fast than some of the ground lug to module systems we used to use.......(and
still use in top of pole mounts)...
Cheers,

-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o

On Tue, Nov 17, 2009 at 1:47 PM, Peter Parrish <
peter.parrish at calsolareng.com> wrote:

> That still works to approximately one clip per rail (actually N-1 clips for
> N modules). - Peter
>
>
>  Peter T. Parrish, Ph.D., President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com
> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
>
>
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Click
> Sent: Tuesday, November 17, 2009 1:09 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Bonding Rails
>
> Yes, that's correct. In my answer I was just rephrasing it to say you'd
> need twice as many WEEBs as you think. As I understand it, the intent of
> this layout is to give the installer two chances to bond each module
> properly to the rail.
>
> Unirac has a similar requirement for its UGC-1s on SolarMount, but in
> their schematic they don't require you to bond to both rails. So if you
> have four modules, you need UGC-1s between A&B, B&C, C&D but you can
> have them all on a single rail. I think it's better to alternate between
> rails anyway: A&B (top rail), B&C (bottom rail), etc.
>
> DKC
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] Bonding Rails
> From: Peter Parrish <peter.parrish at calsolareng.com>
> To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
> Date: 2009/11/17 15:55
>
> > On page 8 it would appear that we need TWO WEEB clips bonding modules A
> and
> > B to rails #1 and #2 and another TWO WEEB clips bonding modules C and D
> to
> > rails #1 and #2, etc. - Peter
> >
> > -----Original Message-----
> > From: re-wrenches-bounces at lists.re-wrenches.org
> > [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave
> Click
> > Sent: Tuesday, November 17, 2009 12:14 PM
> > To: RE-wrenches
> > Subject: Re: [RE-wrenches] Bonding Rails
> >
> > Peter,
> >
> > (1) it appears that per the WEEB installation manual:
> > http://www.we-llc.com/Datasheets/104-0404-000008-008.pdf
> > (page 8) you need to have one WEEB per module rather than one for every
> > other module as you suggest.
> >
> > (2) 690.43 Equipment Grounding.
> > Exposed non-current-carrying metal parts of module frames, equipment,
> > and conductor enclosures shall be grounded in accordance with 250.134 or
> > 250.136(A) regardless of voltage.
> >
> > I guess the latter answer depends on whether your AHJ considers the
> > rails "exposed"-- I would, so in this situation I'd have lugs on each
> > module and each rail.
> >
> > DKC
> >
> > -------- Original Message --------
> > Subject: [RE-wrenches] Bonding Rails
> > From: Peter Parrish <peter.parrish at calsolareng.com>
> > To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
> > Date: 2009/11/17 14:56
> >
> >> We have been using WEEB clips on all of our installations for over a
> >> year now. We include the WEEB data/installation sheets in our permit
> >> package and patiently point out the clips to inspectors who haven't seen
> >> the WEEB system yet.
> >>
> >>
> >>
> >> Two questions:
> >>
> >>
> >>
> >> (1)     For ProSolar rails, can we use one WEEB clip to bond two
> >> adjacent modules (say, modules A and B) on the upper rail (say, rail #1)
> >> and then use a second WEEB clip to bond the next two adjacent modules
> >> (say, modules C and D) on the lower rail (say, rail #2) and then use a
> >> listed lay-in lug (with in our case a WEEB clip) to bond to either rail
> >> #1 or #2 to continue the grounding?
> >>
> >> (2)     If we DON"T use WEEB clips and use the conventional bonding
> >> methodology per module manufacturer's instructions (proper location on
> >> the module, and listed screws, washers and nuts), do we have to ALSO
> >> bond the rails? We have an inspector in Pasadena, CA that is requiring
> >> this, but this is the first time we have been required to do so. Perhaps
> >> in the past year in ignorant bliss we have missed an important
> >> development? Or have we been dodging bullets for seven years and not
> >> even knowing it?
> >>
> >>
> >>
> >> - Peter
> >>
> >> Peter T. Parrish, Ph.D., President
> >> California Solar Engineering, Inc.
> >> 820 Cynthia Ave., Los Angeles, CA 90065
> >> CA Lic. 854779, NABCEP Cert. 031806-26
> >> peter.parrish at calsolareng.com <mailto:peter.parrish at calsolareng.com>
> >> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
> >>
> >
> >>
> >>
> >>
> >>
> >>
> >> ------------------------------------------------------------------------
> >>
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20091117/7b9ff584/attachment-0003.html>


More information about the RE-wrenches mailing list