If the ballasted system is properly designed to withstand the wind
loading (90 mph to 150 mph), I would say that that most definitely
qualifies as "firmly secured".
Is someone actually giving you trouble on this issue, or are you just
thinking ahead?
R. Walters
ray at solarray.com
Solar Engineer
On Oct 26, 2009, at 1:51 PM, Jason Szrom wrote:
> Hello Wrenches…
>
> In typical ballasted systems, the combiner box is mounted on
> unistrut fastened to roof stand-offs which are not fastened to the
> roof. I was wondering what your opinion would be about this in
> reference to the following NEC section:
>
> 110.13 Mounting and Cooling of Equipment
> (A) Mounting. Electrical equipment shall be firmly secured to the
> surface on which it is mounted.
>
> Has anyone ever had a problem with this during an inspection?
>
> Thanks,
>
> Jason Szrom
> Engineer
>
> Solar Energy Systems, LLC
> 1205 Manhattan Ave
> Suite 1210
> Brooklyn, NY 11222
>
> 718-389-1545 x13
> www.solarEsystems.com
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20091026/d576195c/attachment-0003.html>
More information about the RE-wrenches
mailing list