[RE-wrenches] Outback FNDC relay, Flex Net Review
jay peltz
jay at asis.com
Wed Oct 14 22:51:56 PDT 2009
Hi Tump,
However the FNDC has both functions. % start and volt and time start.
So even if the % gets off for some reason, the volt/time should,
repeat, should start it.
I have all but given up on the flexnet. I find for most customers its
too complicated, and while it gives good information, its hard for
folks to read.
And most importantly for me, the AGS function is not reliable. I have
had pretty good luck with the normal AGS, but when hooked to the the
FLEXNET just too unreliable.
And heres the kicker. I talked to the techs at outback about a system
with a problem, and they told me there were having problems with the
flexnet and I should defeat it by setting the start/stop % to 0, great.
jay
peltz power
On Oct 14, 2009, at 4:30 PM, Tump wrote:
>
> I have had issues w/ the FNDC I had to send it back for a reprogram
> I sent the mate back at the same time too. MOST important thing I
> learned is that the battery bank MUST be at a full SOC prior to
> connecting the FNDC otherwise you defiantly will have generator
> issues.
>
> Still having our low voltage “non start” gen problem. Reset all
> parameters in Mate and we will see what happens
> from a customer dated 9/25/09 this customer also has had gen not
> shutting off issues too.
>
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org
> ] On Behalf Of William Miller
> Sent: Wednesday, October 14, 2009 5:28 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Outback FNDC relay, Flex Net Review
>
> Kent:
>
> The manual is not clear as to how this is done. Have you considered
> using a relay in an FX inverter to activate the generator as is done
> in a system without the Flex Net?
>
> Interesting about the SMA claim, but until I hear otherwise, this is
> just a claim.
>
> William
>
>
>
> At 01:25 PM 10/14/2009, you wrote:
>> William,
>>
>> In all of these systems, the Mate's AGS system is being used to
>> control the FNDC's relay. The Mate's AGS port has been selected so
>> that it operates the FNDC's relay rather than using the Aux output
>> on the inverter. The FNDC is providing SOC info to the Mate, but
>> isn't directly controlling the relay.
>>
>> I agree with you about the potential to confuse customers. And
>> about the inaccuracy of battery amp-hour meters in general. But it
>> is interesting that SMA's main claim about the Sunny Island is that
>> it does the best job managing batteries. It does it by keeping
>> track of the battery's SOC.
>>
>>
>> William Miller wrote:
>>> Kent:
>>>
>>> >From the Flex Net DC manual, page 16: "OutBack strongly
>>> recommends using the AGS function of the MATE to control a
>>> generator." I assume from your post, you are using the Auto mode
>>> to have the relay control a generator, a practice that the above
>>> quotation recommends against. This may relate directly to your
>>> problems.
>>>
>>> I have no experience with the Flex Net but I took this opportunity
>>> to review the manual more thoroughly than I have previously. My
>>> conclusion is that the Flex Net is a great tool for the
>>> technically inclined but offers a minimal convenience for the lay
>>> person. The State of Charge function may be a more realistic
>>> method of determining actual state of charge, but if it operates
>>> at all like the E-meter or the Tri-Metric, it is prone to
>>> inaccuracy. The variables associated with individual battery
>>> banks, particularly as they age, make accurate calibration a
>>> moving target. Overall, the Flex net has the potential to
>>> increase customer confusion with a proliferation of synoptic
>>> (overly succinct) menus.
>>>
>>> Again, I call on the technicians in the industry to create a user
>>> interface with the lay person in mind. See previous rant.
>>>
>>> I may find I recommend this system for remote locations so I can
>>> poll statistics and interpret for the client, but I will not train
>>> a client on the use of this unless he or she is particularly
>>> inclined.
>>>
>>> Anyone else have an opinion on the Flex net system?
>>>
>>> William Miller
>>>
>>>
>>>
>>> At 12:13 PM 10/14/2009, you wrote:
>>>> Has anyone besides me had problems using the relay in the Outback
>>>> FNDC? I've had three different customers report that their
>>>> generators failed to turn off.
>>>>
>>>> --
>>>> Kent Osterberg
>>>> Blue Mountain Solar, Inc.
>>>> www.bluemountainsolar.com
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com
>> Version: 8.5.421 / Virus Database: 270.14.16/2435 - Release Date:
>> 10/14/09 06:33:00
>
> Please note new e-mail address and domain:
>
> William Miller
> Miller Solar
> Voice :805-438-5600 Fax: 805-438-4607
> email: william at millersolar.com
> http://millersolar.com
> License No. C-10-773985
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20091014/be8e52cd/attachment-0003.html>
More information about the RE-wrenches
mailing list