Good question. We do use PVC in coastal zones to avoid corrosion. We try
to keep it in the shade, paint it where exposed to UV and support it in
close intervals.
William
At 10:57 AM 10/9/2009, you wrote:
>Except for coastal installations.... where EMT is NOT recommended
>outdoors, PVC browns out and warps, and we should therefore use product X???
>
>R. Walters
><mailto:ray at solarray.com>ray at solarray.com
>Solar Engineer
>
>
>
>
>On Oct 9, 2009, at 11:38 AM, William Miller wrote:
>
>>August:
>>
>>I suggest the use of EMT with proper fittings to protect high voltage,
>>high amperage DC Wiring on rooftops. Sure it is time consuming, but high
>>quality, reliable craftsmanship will always be thus.
>>
>>William Miller
>>
>>
>>
>>