[RE-wrenches] Battery Charger
Mark Dickson
Mark at OasisMontana.com
Mon Sep 28 11:57:57 PDT 2009
Hey there Orion,
I had Quick Charge build a custom charger for us before and it has been
working great. They can build just about anything you have in mind. We
bought ours through Derek @ IBE batteries.
Otherwise I believe the best solution is the one you mentioned, just have
the Genewreck power loads directly through a x-fer switch.
Best regards,
Mark Dickson
Oasis Montana Inc.
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Orion
Thornton
Sent: Monday, September 28, 2009 12:43 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Battery Charger
Wrenches,
We recently installed a grid-tie battery backup system using two Outback
GVFX 3648 inverters. The client has an existing Generac backup generator, 8
kW @ 240VAC. From the beginning we told the client that the power quality
from the Generac may not be within tolerance to integrate with the grid-tie
inverters and charge batteries. This assumption was confirmed today when we
commissioned and tested the system. The output frequency of the Generac was
58 hz.
To get to the point does anyone have a battery charger they recommend for
this application?-8 kW @ 240VAC generator output to 48VDC battery bank. Or
maybe another suggestion to be able to integrate the generator into the
system, we are also planning on manually transferring the generator output
to power the critical loads if an inverter goes down.
It also seems that the dc genset controls through the mate would be the best
way to control the battery charger-any thoughts?
Thanks in advance for any input.
Orion Thornton
Project Manager
Independent Power Systems
NABCEP Certified PV Installer
(W) 406.587.5295
(C) 406.249.9912
www.solarips.com <http://www.solarips.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090928/2a6710a5/attachment-0003.html>
More information about the RE-wrenches
mailing list