I think that the 250kW Florida Power & Light array in Sarasota, FL was 
installed on a ground cover (over a landfill) like the SIT solution, and 
that it was just done with PowerGuard.

-------- Original Message --------
Subject: Re: [RE-wrenches] ballasted roof rack - on the ground?
From: Joel  Davidson <joel.davidson at sbcglobal.net>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date: 2009/8/21 10:14

> Geoff,
>  
> Solar Integrated Technologies adheres its panels on ground covers 
> over landfills to capture landfill gases and separately produce PV 
> electricity. Perhaps a wrench with Powerlight experience can tell us why 
> rigid modules are not laid on a ground cover.
>  
> Joel Davidson
> 
>     ----- Original Message -----
>     *From:* Geoff Greenfield <mailto:geoff at third-sun.com>
>     *To:* RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
>     *Sent:* Thursday, August 20, 2009 8:35 PM
>     *Subject:* [RE-wrenches] ballasted roof rack - on the ground?
> 
>     esteemed wrenches (or just steamed if youve been out in the hot lately)
> 
>     I'm curious why more folks don't use the same flat roof ballasted
>     rack approach for large ground mounts?  Geotech weed barier and off
>     we go...  my initial calcs sat its a cost saver... my instinct says
>     it viable, but my other instinct says "if it were this easy I would
>     see it all the time (and I've never seen it)
> 
>     what's up?  frost heave/instability?  wav-i-ness of the ground?
>     better performance at steep angle worth all the extra cost (not
>     according to my pencil with today's mod costs).  Thoughts? 
> 
>     For a brighter energy future,
> 
>     Geoff Greenfield
>     President
>     Third Sun Solar & Wind Power Ltd.
>     340 West State Street, Unit 25
>     Athens, OH 45701
> 
>     740.597.3111     Fax 740.597.1548
>     www.Third-Sun.com
> 
>     Clean Energy - Expertly Installed
> 
> 
> 
> 
> 
> 
>     ----- "Dave Click" <daveclick at fsec.ucf.edu> wrote:
>      > Thanks all.
>      >
>      > It was my understanding that we should still be running the
>     conductors
>      > of the same circuit through the same raceway, even if it is the
>     DC input
>      > into the inverter since that DC oscillates slightly (nowhere near as
>      > much as AC). I wasn't concerned about eddy currents in the FNMC of
>      > course but the metal box itself, a concern being voiced on this list
>      > before. I'd be more concerned about this if it were a 1MW inverter
>      > rather than a 7kW, but still.
>      >
>      > Thanks for the info on the GEC tap and I'm glad the split bolts
>     work here.
>      >
>      > The conduit in question doesn't seem to be there just for physical
>      > protection; the wire runs from the east end of the array for
>     100'+ and
>      > only the last 3' are in conduit. If it were only for protection
>     I'd be
>      > fine with it being open-ended on both ends, but since it's there
>     to feed
>      > the conductors into the box, that's why I was treating it as a
>     regular
>      > conduit that required a cord grip at the other end. Where do
>     others make
>      > the distinction?
>      >
>      > Thanks,
>      > DKC
>      >
>      > -------- Original Message --------
>      > Subject: Re: [RE-wrenches] DC positive and negative in same conduit,
>      > other inspection issues
>      > From: Kelly Keilwitz, Whidbey Sun &  Wind <kelly at whidbeysunwind.com>
>      > To: RE Wrenches listserve <re-wrenches at lists.re-wrenches.org>
>      > Date: 2009/8/19 21:10
>      >
>      > > Dave,
>      > > Only GEC's are subject to the "continuous" rule (250.64C). It
>     sounds like
>      > > your are talking about an EGC tapped from the GEC.
>      > >
>      > > When splicing PV GEC's required under 690.47D, either together
>     (from
>      > > separated arrays) or to the existing AC GEC (if close enough),
>     we have been
>      > > allowed to use split bolts instead of irreversible splices, per
>     250.64D1,
>      > > "Grounding Electrode Conductor Taps" (at end of paragraph).
>     I.E., the
>      > > "continuous" rule is only being applied to the main GEC.
>      > >
>      > > I agree with Kurt on the LTNMF being used only as extra (not
>     required) wire
>      > > protection for the USE-2. We often do this when running PV
>     conductors
>      > > between short separations in modules or rails. I would think
>     that only
>      > > temperature and fill corrections would apply - and only if the
>     length
>      > > requires.
>      > >
>      > > -Kelly
>      > >
>      > > Kelly Keilwitz, P.E.
>      > > Whidbey Sun & Wind, LLC
>      > > Renewable Energy Systems
>      > > NABCEP Certified PV Installer
>      > > 987 Wanamaker Rd,
>      > > Coupeville, WA 98239
>      > > PH & FAX 360-678-7131
>      > > sunwind at whidbeysunwind.com
>      > >
>      > > On 8/19/09 2:41 PM, "Dave Click" <daveclick at fsec.ucf.edu> wrote:
>      > >
>      > >> For the grounding electrode wiring, it seems that it's fine to
>     me since
>      > >> they ran the continuous #6 to each rail and then to the rod,
>     qualifying
>      > >> as the 690.47(D) supplemental electrode. But the split bolts
>     tapping
>      > >> that GEC to "ground the disconnect," these are required to be
>      > >> irreversible connections to the ground bus in that disconnect,
>     right?
>      > >
>      > >
>      > >  
>      > >
>      > >
>      > >
>      > > _______________________________________________
>      > > List sponsored by Home Power magazine
>      > >
>      > > List Address: RE-wrenches at lists.re-wrenches.org
>      > >
>      > > Options & settings:
>      > >
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>      > >
>      > > List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>      > >
>      > > List rules & etiquette:
>      > > www.re-wrenches.org/etiquette.htm
>      > >
>      > > Check out participant bios:
>      > > www.members.re-wrenches.org
>      > >
>      > >
>      > _______________________________________________
>      > List sponsored by Home Power magazine
>      >
>      > List Address: RE-wrenches at lists.re-wrenches.org
>      >
>      > Options & settings:
>      > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>      >
>      > List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>      >
>      > List rules & etiquette:
>      > www.re-wrenches.org/etiquette.htm
>      >
>      > Check out participant bios:
>      > www.members.re-wrenches.org
>      >
>      >
> 
>     ------------------------------------------------------------------------
> 
>     _______________________________________________
>     List sponsored by Home Power magazine
> 
>     List Address: RE-wrenches at lists.re-wrenches.org
> 
>     Options & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
> 
>     Check out participant bios:
>     www.members.re-wrenches.org
> 
> 
> ------------------------------------------------------------------------
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 



More information about the RE-wrenches mailing list