[RE-wrenches] XW6048 parts problem
Drake Chamberlin
drake.chamberlin at redwoodalliance.org
Wed Aug 5 06:49:26 PDT 2009
Hi Peter,
The Outback inverter will not regulate battery charge while AC
coupled. The SMA is the only system designed to give a regulated
charge to batteries in the AC coupled mode. The Outback axillary
relay can be used to drive a relay that will disconnect the input to
the inverter, to regulate battery charge when grid is down. I like
an "Ice Cube Rely" (such as Idec) to control a contactor. The coil
of the Idec uses very little power.
Why did you gravitate toward Xantrex from Outback?
Drake
At 09:25 PM 8/4/2009, you wrote:
>I would like to start a thread on AC-coupled grid tied battery
>backup systems. We do a fair number of GTBBSs (four to five a year)
>and I have gravitated from the Outback solution to the Xantrex XW
>solution. I am not happy with the XW product and especially not
>happy with Xantrex's post sales technical support. I know I have
>more to learn about these puppies in general, so I am genuinely
>disappointed with the uneven TS from Xantrex.
>
>I also had this nagging feeling that the heart of a GTBBS should be
>the tried and true high voltage inverter. Enter the SunPower
>positive ground requirement, and now an AC coupled system seems the
>best solution.
>
> From the white paper that Outback sent me, there was no mention of
> a heavy duty relay. Doesn't the Outback inverter regulate the
> battery charge control?
>
>Has anyone tried to order a SunWize "Solar Ready Battery Assembly"
>without the charge controller (e.g. P/N SRB3.6). It would seem that
>this is a nice package for small energy needs (13 to 26 kWh of
>battery backup).
>
>- Peter
>[]
>Peter T. Parrish, Ph.D., President
>California Solar Engineering, Inc.
>820 Cynthia Ave., Los Angeles, CA 90065
>CA Lic. 854779, NABCEP Cert. 031806-26
><mailto:peter.parrish at calsolareng.com>peter.parrish at calsolareng.com
>Ph 323-258-8883, Mobile 323-839-6108, Fax
>323-258-8885
>
>
>
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
>Sent: Tuesday, August 04, 2009 5:55 PM
>To: jryago at netscape.com; RE-wrenches
>Subject: Re: [RE-wrenches] XW6048 parts problem
>
>Jeff:
>
>I have a spare. They are not kept in the socket but are loose in a
>bag. Send me your mailing address off list. I leave tomorrow for a
>week, so I hope I see your address before I go.
>
>William
>
>
>
>
>At 04:59 PM 8/4/2009, you wrote:
>
>Just completed a large residential grid/gen/solar/battery system
>using a XW6048 inverter.
>
>We are using a SunnyBoy inverter at the array and doing an AC
>coupled backfeed. To do this we have installed a heavy duty relay
>in the output of the SunnyBoy, and are using the aux. relay contacts
>on the XW unit to close this relay when battery voltage is at high
>limit (during no load power outage to prevent over-charging)
>
>Not sure if we lost it during installation, if it shook loose in
>shipment and fell out, or was missing to begin with, but to connect
>to the aux. contacts in th XW requires a very small green flat 5-pin
>connector which is missing.
>
>I contacted multiple people at Xantrex and their service center,
>waded through their web site, and finally talked to a service
>tech. He advised that "he was looking for an extra one of these
>connectors 6 months ago and still has not received it, as these
>compoments are made and assembled in China and they do not stock
>anything that is considered an assembly part used in China to build
>their units."
>
>First, I did not realize these inverters were being assembled in
>China, and second, who ever heard of not stocking a replacement part
>just because its made in China. If that were true, 95% of
>everything sold today in US would not be able to order replacement parts.
>
>Anybody out their know if there is a Radio Shack type supplier where
>I can order a bag of these and get on with the system startup and my life?
>
>Thanks,
>
>Jeff Yago
>
>_____________________________________________________________
>Netscape. Just the Net You Need.
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>No virus found in this incoming message.
>Checked by AVG - www.avg.com
>Version: 8.5.392 / Virus Database: 270.13.43/2281 - Release Date:
>08/04/09 05:57:00
>
>Please note new e-mail address and domain:
>
>William Miller
>Miller Solar
>Voice :805-438-5600 Fax: 805-438-4607
>email: william at millersolar.com
>http://millersolar.com
>License No. C-10-773985
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090805/546a3a4a/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 12bdf9.gif
Type: application/octet-stream
Size: 4262 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090805/546a3a4a/attachment-0006.obj>
More information about the RE-wrenches
mailing list