I also had a faulty 15 A breaker on an array with less than 11 amps
short circuit current. It tripped intermittently maybe 4 or 5 times
over a year, so we swapped it out. Perhaps they had a bad batch?
I was going to test it at the shop, but didn't have a chance yet.
R. Walters
Solarray.com
NABCEP # 04170442
On Jul 27, 2009, at 6:04 PM, Kent Osterberg wrote:
> Allan,
>
> I've had trouble with breakers opening when they shouldn't. On an
> array of two strings of Mitsubishi 175s (Isc = 7.9A) I had two 15-A
> breakers open. Last week, I had a low-power call from a customer
> with three strings of Evergreen 190s (Isc = 7.1A); one 15-A breaker
> in the combiner was open. Most of my installs are around 3000 ft
> elevation, so the irradiance is possibly a little higher than
> normal, but not by enough that it should be an issue for 15-amp
> breakers. If this is a wide-spread problem, I'd expect others on
> this list to have noticed.
>
> As others have mentioned, it is important to take precautions to
> make sure that stranded wires are well tightened in these
> breakers. I tighten, wiggle, re-tighten, and then check again
> later. On systems where I've had breakers open, loose connections
> haven't been the issue.
>
> Kent Osterberg
> Blue Mountain Solar, Inc.
> www.bluemoutainsolar.com
>
>
> Allan Sindelar wrote:
>>
>> I have had no problems to date, Kent. Can you be more specific as
>> to what
>> problems you have had?
>>
>> Allan Sindelar
>> Allan at positiveenergysolar.com
>> NABCEP Certified Photovoltaic Installer
>> EE98J Journeyman Electrician
>> Positive Energy, Inc.
>> 3201 Calle Marie
>> Santa Fe, New Mexico 87507
>> 505 424-1112
>> www.positiveenergysolar.com
>>
>> -----Original Message-----
>> Is it just me, or have other wrenches had problems with the CBI
>> circuit
>> breakers used in the Outback or Midnite combiner boxes?
>>
>> Kent Osterberg
>> Blue Mountain Solar, Inc.
>> http://www.bluemountainsolar.com/
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090728/fb8a17b4/attachment-0003.html>
More information about the RE-wrenches
mailing list