[RE-wrenches] myers hubs
William Miller
william at millersolar.com
Fri Jul 24 11:22:04 PDT 2009
August:
Thanks for the reply. The use of the compression EMT connectors still
requires a threaded hub to be considered rain-tight. These do not solve
the problem of how to connect PVC conduit to a plastic box, maintain
rain-tight status and avoid introducing a metallic fitting that requires
bonding. I was hoping to learn about a new fitting to solve this problem.
One of my wholesalers claims the use of a sealing locknut on a standard PVC
male adapter is considered raintight. I am skeptical. Does anyone know if
this assertion is backed with code language?
William Miller
At 11:14 AM 7/24/2009, you wrote:
>Sorry, that first link was for a coupling. Here is a connector link:
>
><http://www.arlcatalog.com/EMT/EMT%20Rain%20Tight%20Compression%20Connectors%20with%20Insulated%20Throat.htm>http://www.arlcatalog.com/EMT/EMT%20Rain%20Tight%20Compression%20Connectors%20with%20Insulated%20Throat.htm
>
>-August
>
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of August Goers
>Sent: Friday, July 24, 2009 10:15 AM
>To: 'RE-wrenches'
>Subject: Re: [RE-wrenches] myers hubs
>
>William,
>
>See:
><http://www.arlcatalog.com/EMT/EMT%20Rain%20Tight%20Compression%20Couplings.htm>http://www.arlcatalog.com/EMT/EMT%20Rain%20Tight%20Compression%20Couplings.htm
>
>These fittings are nice because the steel is tinted blue to help assure
>that installers don't use non-listed fittings.
>
>When I referred to "wet-loc" I simply meant an EMT compression coupling
>specifically labeled for use in wet locations. The particular connector I
>have in front of me has "WET LOC" printed on it. San Francisco code
>officials check to make sure that the fittings we use outdoors are listed
>for use in wet locations.
>
>-August
>
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
>Sent: Friday, July 24, 2009 9:20 AM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] myers hubs
>
>August:
>
>I am familiar with the Myers hubs. My question was referring to the
>"wet-loc" connector you alluded to. Who makes those?
>
>William Miller
>
>
>
>At 09:00 AM 7/24/2009, you wrote:
>William,
>
>Here is a Thomas&Betts PN:
>
><http://www.tnb.com/ps/fulltilt/index.cgi?part=H050CP>http://www.tnb.com/ps/fulltilt/index.cgi?part=H050CP
>
>Page 15 (A-18) of this pdf explains the hub in detail:
>
><http://tnblnx3.tnb.com/emAlbum/albums/tc_us/tc_1_rigidoverspec.pdf>http://tnblnx3.tnb.com/emAlbum/albums//tc_us/tc_1_rigidoverspec.pdf
>
>-August
>
>
>
>August Goers
>
>Luminalt Energy Corporation
>O: 415.564.7652
>M: 415.559.1525
>F: 650.244.9167
><http://www.luminalt.com/>www.luminalt.com
><mailto:august at luminalt.com>august at luminalt.com
>
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
>Sent: Friday, July 24, 2009 8:42 AM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] myers hubs
>
>August:
>
>Who manufactures these connectors? Do you have a part number?
>
>Marco:
>
>Don't forget that if you do not have splices in an outdoor J box, and if
>your wire is wet location rated, you are not required to use Nema 3R boxes
>and fittings.
>
>William Miller
>
>
>
>
>
>At 08:27 AM 7/24/2009, you wrote:
>
>Marco,
>
>Interesting question. May I ask why you want to use a Myers hub rather
>than a standard wet-loc outdoor connector?
>
>My understanding is that Myers hubs are used for weatherproofing and
>bonding (when used with a metal box) because the inside nut is serrated.
>See NEC 250.92(B)(2) and 314.15(A).
>
>Anyone agree or disagree with me?
>
>-August