August:
Who manufactures these connectors? Do you have a part number?
Marco:
Don't forget that if you do not have splices in an outdoor J box, and if
your wire is wet location rated, you are not required to use Nema 3R boxes
and fittings.
William Miller
At 08:27 AM 7/24/2009, you wrote:
>Marco,
>
>Interesting question. May I ask why you want to use a Myers hub rather
>than a standard wet-loc outdoor connector?
>
>My understanding is that Myers hubs are used for weatherproofing and
>bonding (when used with a metal box) because the inside nut is serrated.
>See NEC 250.92(B)(2) and 314.15(A).
>
>Anyone agree or disagree with me?
>
>-August
>
>August Goers
>
>
>Luminalt Energy Corporation
>O: 415.564.7652
>M: 415.559.1525
>F: 650.244.9167
><http://www.luminalt.com/>www.luminalt.com
><mailto:august at luminalt.com>august at luminalt.com
>
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco
>Sent: Thursday, July 23, 2009 5:36 PM
>To: 'RE-wrenches'
>Subject: [RE-wrenches] myers hubs
>
>Anyone know if Myers hubs are acceptable to use outdoors to attach to a
>non-metallic enclosure?
>
>thanks,
>marco
>