Who manufactures these connectors? Do you have a part
number?<br><br>
Marco:<br><br>
Don't forget that if you do not have splices in an outdoor J box, and if
your wire is wet location rated, you are not required to use Nema 3R
boxes and fittings.<br><br>
William Miller<br><br>
<br><br>
<br><br>
At 08:27 AM 7/24/2009, you wrote:<br>
</font><blockquote type=cite class=cite cite><font face="arial" size=2>Marco,<br>
<br>
Interesting question. May I ask why you want to use a Myers hub rather
than a standard wet-loc outdoor connector?<br>
<br>
My understanding is that Myers hubs are used for weatherproofing and
bonding (when used with a metal box) because the inside nut is serrated.
See NEC 250.92(B)(2) and 314.15(A). <br>
<br>
Anyone agree or disagree with me? <br>
</font><font face="arial" size=2 color="#000080"> <br>
-August<br>
<br>
<b>August Goers<br>
</b> <br>
<br>
Luminalt Energy Corporation<br>
O: 415.564.7652<br>
M: 415.559.1525<br>
F: 650.244.9167<br>
<a href="http://www.luminalt.com/">www.luminalt.com</a><br>
<a href="mailto:august@luminalt.com">august@luminalt.com</a><br>
<br>
<hr>
<div align="center"></font></div>
<font face="tahoma" size=2><b>From:</b>
re-wrenches-bounces@lists.re-wrenches.org [<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Marco<br>
<b>Sent:</b> Thursday, July 23, 2009 5:36 PM<br>
<b>To:</b> 'RE-wrenches'<br>
<b>Subject:</b> [RE-wrenches] myers hubs<br>
</font><font face="Times New Roman, Times" size=3> <br>
</font><font face="arial" size=2>Anyone know if Myers hubs are acceptable to use outdoors to attach to a non-metallic enclosure?<br>
</font><font face="Times New Roman, Times" size=3> <br>
</font><font face="arial" size=2>thanks,<br>
marco<br>
</font><font face="Times New Roman, Times" size=3> </font></blockquote></body>
</html>