Troy:
Let me guess... They want it right away and cheap, too. Generally
speaking, this is an impractical request. Electrically operated circuit
breakers or 20 A relays and controllers are expensive and complicated. One
thing to learn in this trade is when to try and talk a client out of a bad
idea, and when a client has such wacky ideas that it is best to walk away.
I could, however, suggest two ways to do this:
1. Use two inverters and set the LBCO for one high. Connect one to
critical loads and one (with the high LBCO) to non-critical loads. When
the batteries start getting low, the non-critical-loads inverter shuts
down, leaving the critical-loads inverter running.
Realize that you now need four load centers: Grid, generator (you have
recommended a generator so they can use their wide screen TV during a wind
storm, correct?), non-critical loads and critical loads. This type of
design gets complicated fast. Will the AHJ be able to track this? Set a
clause that allows you to collect hourly fees when they require three
different meetings and three re-writes of the permit application.
2. Use an Outback with external relays to shut off loads when the battery
voltage falls below a certain point. This is a crude approach, the
parameters are not flexible (hard coded delay values) and it requires
custom built relay panels, time consuming, expensive and a potential
service problem.
Either system is actuated on battery voltage rather than loads. Inverters
I am familiar with have relays and internal controls that operate based a
set-able battery voltages, but I know of none that has a programmable relay
to actuate at a certain load level. In addition, loads change so rapidly
that this type of switching would be erratic. Loading is a component of
battery voltage, anyway, so you are including that indirectly.
Good Luck,
William Miller
At 07:41 PM 6/23/2009, you wrote:
>Hi folks,
>
>I need an inverter/charger/controller solution for a grid connect
>house that:
>1. grid-connects (net-meters)
>2. Islands off of the battery in outages (whole house UPS)
>3. Feeds into the whole house breaker, so the whole house is backed up
>4. Shuts down less important breakers as needed, if the load for the
>whole house is over the inverter limit
>
>Instead of guessing which breakers are important to put on a battery
>backed up sub-panel, my client would like the whole house backed up.
>But of course, can't guarantee that the house won't be drawing too
>much for a 6000 Watt inverter at any given time. So would like to have
>the system intelligently remove less important breakers until the
>system is below the inverter operation wattage.
>
>Anyone know of a inverter system that is smart like that?
>
>Troy Harvey
>---------------------
>Heliocentric
>801-453-9434
>taharvey at heliocentric.org