[RE-wrenches] AC coupled relay
Kirk Herander, VSE
kirk at vtsolar.com
Wed Jun 3 11:05:08 PDT 2009
I have done it with a SQD 60a, 240 vac contactor. The coil is 120 vac. It is
driven by a secondary 12vdc relay sending 120 ac to the coil. The coil of
the dc relay is driven by the 12 vdc auxiliary output of the Outback FX
inverter. I use the contactor and dc relay normally closed contacts. They
open when the inverter energizes the dc relay.
Kirk Herander
Vermont Solar Engineering
802.863.1202
NABCEP(tm) Certified Solar Installer
NYSERDA-eligible Installer
VT Solar Incentive Program Partner
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jeff Yago
Sent: Wednesday, June 03, 2009 9:35 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupled relay
What specific supplier, model number, and brand relay have you found to be
perfect to isolate the inverter AC output to the sub-panel of a
battery-based inverter in an AC coupled system?
This will be in the 20 to 30 amp 240 VAC contact range. Also, do you
normally set it up as N.C. or N.O. for fail-safe reasons? Coil voltage 12
vdc or 120 vac?
Thanks,
Jeff Yago