jay peltz jay at asis.com
Mon Jan 19 08:12:28 PST 2009


Hi Jeff,

1. if the distances are really far why not run the DC from the panels  
to the inverter, higher voltage, smaller wire.
2. if you use the XW then yes you will be running the AC from the SB  
to the sub panel, this will feed the inverter and cause it to charge,  
which you will need to put a relay disconnect on.  Use a SS relay on  
the AC side from the SB connected to one of the XW aux relays. So you  
are not really installing a load but a high battery/SB relay.
3.  The XW will not see this as AC in.  If you hook it up that way to  
AC in it won't work except if the grid is on.  No grid no SB.  But  
then also no battery charging.

Hope this helps,

jay

peltz power

On Jan 18, 2009, at 9:31 PM, Jeff Yago wrote:

> I know this subject has come up before, but there have been several  
> different suggested ways to handle the problem and I was hoping for  
> easiest.  We install lots of both on grid and off grid systems.   
> However, we have a client that will require a ground mounted array  
> much futher away from the inverter and batteries in the garage than  
> we normally would want to do since the voltage drop for this long  
> distance would be excessive at low voltage even with large cables.   
> We have decided to locate a weather-proof sunnyboy grid-tie inverter  
> at the array, and supply 120/240 volts to the critical loads sub- 
> panel which is supplied by a Xanrex XW inverter and battery bank in  
> the garage. I realize there are several design issues here when the  
> grid is down,  since we want the grid-tie inverter to remain on but  
> be blocked from the grid by the Xantrex inverter.
>
> The question is, what is the best way to keep a load on the sunnyboy  
> since it will not be grid connected during an outage.  Also, is  
> there a best way to feed the output from the Sunnyboy to the Xantrex  
> that does not just power the sub-panel loads during an outage, but  
> also will re-charge the battery bank through the Xanrex?
>
> If you back-feed the Xanrex from the sub-panel it is normally  
> supplying with output from the Sunnyboy, will the Xanrex see this  
> input and think the grid is up and be able to re-charge the battery  
> bank?
>
> Will we need any separate transfer switches or power relays?
>
> Thanks,
>
> Jeff Yago
>
> _____________________________________________________________
> Netscape.  Just the Net You Need.
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>




More information about the RE-wrenches mailing list