[RE-wrenches] Outback VFX input voltage cycling

Darryl Thayer daryl_solar at yahoo.com
Sat Dec 27 08:15:05 PST 2008


It sounds like the AC charge current is set to high, with the batteries being low the inverter charge rate is overloading the gen set. The gen set voltage drops and the inverter releases the genny and the voltage returns, the inverter reloads the genny and the cycle repeats.  If this worked before the gen set need attension, if not (changes to settings having occured or batteries just to low) reduce the AC charge current.  
Daryl


--- On Sat, 12/27/08, Cvsolar2 at aol.com <Cvsolar2 at aol.com> wrote:

> From: Cvsolar2 at aol.com <Cvsolar2 at aol.com>
> Subject: Re: [RE-wrenches] Outback VFX input voltage cycling
> To: re-wrenches at lists.re-wrenches.org
> Date: Saturday, December 27, 2008, 8:45 AM
> Sounds like a generator issue. Maybe a connection. maybe a
> generator control 
> board.  The generator out voltage test, are you sure
> you're seeing the true 
> generator out? Or are you seeing the inverter (i.e., a Gen.
> Service Receptacle). 
> Maybe a gen set tune up? Sounds like the inverter is fine.
> my 2 cents. db
> 
> Dan Brown
> President
> Foxfire Energy Corp.
> Renewable Energy Systems 
> (802)-483-2564
> www.Foxfire-Energy.com
> NABCEP #092907-44
> 
> 
> **************
> One site keeps you connected to all your 
> email: AOL Mail, Gmail, and Yahoo Mail. Try it now. 
> (http://www.aol.com/?optin=new-dp&icid=aolcom40vanity&ncid=emlcntaolcom00000025)
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org


      



More information about the RE-wrenches mailing list