[RE-wrenches] Outback VFX input voltage cycling
    jay peltz 
    jay at asis.com
       
    Sat Dec 27 08:58:17 PST 2008
    
    
  
Hi Ron,
Almost for sure its the genny.  What type and when was it last  
serviced and how many hours does it have?
if the voltage is going all over the place really quickly then its not  
connecting to the inverter at all.
So here is a test that might help.  Turn on a resistive load such as a  
floor heater ( size depends on the generator) to lock in the voltage.   
At this point if the voltage is constant, then the inverter might  
connect.
If this works, then the problem is most likely the genny, which case  
its needs some work.
jay
peltz power
On Dec 26, 2008, at 8:43 PM, R Young wrote:
> I'm having a problem with an Outback VFX3524 inverter installed on  
> an E-panel in a remote off-grid location. Voltage at the inverter  
> input terminals is fluctuating between 110 & 140+ volts  
> continuously. AC in will not connect so batteries can't charge.  
> Output voltage measured at the inverter output terminals is steady  
> at 122v.  When all household loads are turned off the input terminal  
> voltage stabilizes but AC In still does not connect.
>
> Generator does not seem to be at fault as output measured at the  
> gen. is stable even under load. System was working for about 1 1/2  
> years but under new ownership has been badly monitored and batteries  
> have become totally discharged.
>
> I'm trying to determine if this is a circuit board problem so I can  
> perform a rescue mission by pulling some boards from an in-stock  
> inverter, Outback tech support are on holidays. Anyone had a similar  
> problem?
>
> Ron Young
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
    
    
More information about the RE-wrenches
mailing list