The 2008 NEC broaden this 120% allowance to include commercial facilities.
There are some additional requirements to be aware of in order to use the
120% allowance.
On 12/5/08 7:10 PM, "Mark Frye" <markf at berkeleysolar.com> wrote:
> 120% allowance is only "..For a dwelling unit....".
>
> Clearly this is a load side Point of Connection. If it is a "dwelling unit""
> then the 120% allowance is applicable. If it is not a "dwelling unit", then
> there is no room to connect under NEC 2008.
>
> Mark Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City, CA 95959
> (530) 401-8024
> www.berkeleysolar.com <http://www.berkeleysolar.com/>
>
>
>
>
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of August Goers
> Sent: Friday, December 05, 2008 5:01 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] load side taps and NEC 240.21
>
> Jerry -
>
> A line tap typically occurs between the utility meter and the main breaker -
> not after the main breaker on the load side. It seems that you are describing
> a load side tap which follows the 120% rule under 2008 NEC; I might be
> misunderstanding the situation. Please clarify. There are few folks out there
> who are able handle these large commercial grade interconnections and I think
> it is well worth discussing.
>
> Good luck! -August
>
>
> August Goers
>
> Luminalt Energy Corporation
> 4000 Irving Street
> San Francisco, CA 94122
>
>
> Office: 415.564.7652
> Mobile: 415.559.1525
> august at luminalt.com
> www.luminalt.com
>
>
>
> From: William Miller <wrmiller at charter.net>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Sent: Friday, December 5, 2008 4:11:15 PM
> Subject: Re: [RE-wrenches] load side taps and NEC 240.21
>
> Jerry:
>
> At a recent John Wiles seminar, John declared that this scenario is not a
> tap and is therefore not covered under the tap rule. This was news to me,
> but Wiles is considered some sort of guru in compliance discussions.
>
> William Miller
>
>
> At 03:43 PM 12/5/2008, you wrote:
>
>> >Wreches,
>> >
>> >
>> >I have a system where we are tapping onto the bus bars of a 1200 amp panel
>> >fed by a 1200 amp main breaker. The easy place to tap onto the bus bars
>> >is the load side of the breaker using the existing bolts.
>> >
>> >
>> >The inverter and utility fused disco are about 200 ft away, and the tap
>> >conductors travel about15ft in EMT conduit before leaving the
>> >building. After that the circuit is outdoors. NEC 240.21(B)5 allows taps
>> >of unlimited length for conductors located outside of a building, except
>> >at the point of load (in this case supply) termination.
>> >
>> >
>> >Can 20ft of conductor inside the building be covered by being "at the
>> >point of load termination", or do I have to comply with NEC 240.21(B)2 and
>> >have an OCPD within 25'?
>> >
>> >
>> >The construction foreman for this project is buddies with the inspector,
>> >so getting a signed permit won't be a problem but I want this to be a code
>> >compliant system. Can anyone lend some insight to the spirit of
>> >240.21(B)2 and 5?
>> >
>> >
>> >Sorry if this has been discussed before, but searching didn't yield any
>> >results.
>> >
>> >
>> >Best,
>> >
>> >Jerry Caldwell
>> >
>> >Recurrent Energy
>> >
>> >_______________________________________________
>> >List sponsored by Home Power magazine
>> >
>> >List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> >Options & settings:
>> >http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> >List-Archive:
>> >http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> >
>> >List rules & etiquette:
>> >www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> >
>> >Check out participant bios:
>> >www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> David Brearley, Technical Editor
> SolarPro magazine
> NABCEP Certified PV Installer
> david.brearley at solarprofessional.com
> Direct: 541.261.6545
> Fax: 541.512.0343
>
> Visit our Web site at solarprofessional.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081205/6be76624/attachment-0004.html>
More information about the RE-wrenches
mailing list