[RE-wrenches] Summer cooling
Darryl Thayer
daryl_solar at yahoo.com
Wed Aug 20 15:19:04 PDT 2008
HI DAna
I worked on a super insulated house, latest version was 4500 sq. ft that cools with a 3 ton AC, But most of the coolong is from the thermal mass. whole house ventalation and proper operation of air changes. none during the day and lots at night. (if you want to be warmer tomorrow set up the thermostat today). I think they used there AC twice this year. But there is a caution: with humid regions, mold from dampness is possible.
Darryl
--- On Wed, 8/20/08, Dana <dana at solarwork.com> wrote:
> From: Dana <dana at solarwork.com>
> Subject: Re: [RE-wrenches] Summer cooling
> To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
> Date: Wednesday, August 20, 2008, 5:03 PM
> I have always wanted to do a super insulated house design
> that had a large central masonry mass or floor slab with
> heat tubing that you could cool in the summer during the
> nighttime and solar heat in the winter with solar. Or an
> earth tube air duct system that you could pull cool night
> air through that would cool the slab. I built a Passive
> Annual Heat Storage home 16 years ago that kept the house at
> 68 F during the summer in western Washington. I was very
> comfortable. Any thoughts ?
>
>
>
> Thanks -
>
>
>
> Dana Orzel
>
>
>
> Great Solar Works, Inc
>
> www.solarwork.com
>
> E - dana at solarwork.com
>
> V - 970.626.5253
>
> F - 970.626.4140
>
> C - 970.209.4076
>
>
>
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf
> Of Tom Elliot
> Sent: Wednesday, August 20, 2008 3:57 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] offgrid system question
>
>
>
> Thank you Jeff, for asking the obvious. I've been agog
> that no one seemed to think this was a nutty situation for
> an off-grid home.
>
>
>
> T.
>
>
>
>
>
> ----- Original Message -----
>
> From: Jeff Yago <mailto:jryago at netscape.com>
>
> To: RE-wrenches
> <mailto:re-wrenches at lists.re-wrenches.org>
>
> Sent: Wednesday, August 20, 2008 10:57 AM
>
> Subject: Re: [RE-wrenches] offgrid system question
>
>
>
> I may be out of line here, but most of these comments have
> been related to making the right program settings and
> startup surge current issues. I did not read any comments
> that this client is nuts to try and run a 3.5 ton air
> conditioner from a solar off-grid system, let alone a system
> with such a very small capacity.
>
>
>
> I would be surprised if this small existing solar array and
> batteries can keep up with the regular loads like lights,
> kitchen appliances, refrigerators, and entertainment
> equipment, let alone also running a central air conditioner.
> .
>
>
>
> I would not just debate the problems of surge current, I
> would like to know how this little solar system is going to
> keep up with the constant load of approx. 4,000 watts for
> the AC unit plus another 500 watts for the air handling unit
> which he did not mention. With a constant drain of 4,500
> watts, just how long do you think this battery bank will
> last? For most locations, during peak summer days a
> typical AC unit needs to run constantly 12 to 16 hours per
> day.
>
>
>
> I would be interested in hearing from others on this, but
> here in the humid and hot east it is not possible to provide
> air conditioning for an off-grid home unless we are just
> cooling one or two rooms with a low energy Sanyo type split
> system in the 1/2 to 3/4 ton range. Of course if you have
> enough solar modules and batteries you could run anything,
> but can you afford it?
>
>
>
> We do lots of off-grid systems and the first thing we tell
> clients is to not even think about having air conditioning,
> electric hot water heaters, or electric clothes dryers
> unless they have a really big bag of money.
>
>
>
> Jeff Yago
>
>
>
>
>
> _____
>
>
> Netscape. Just the Net You Need.
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.138 / Virus Database: 270.6.6/1624 - Release
> Date: 8/20/2008 7:11 PM
> _____
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
> No virus found in this outgoing message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.138 / Virus Database: 270.6.6/1624 - Release
> Date: 8/20/2008 7:11 PM
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
More information about the RE-wrenches
mailing list