350 feet to barn- grounding [RE-wrenches]
Steve Johnson
stevejohnson at comcast.net
Sun Jun 29 17:55:41 PDT 2008
Ok already, I put it back in. I did reduce the ground size, from what I
had, as per 690.45 A (Increases in equipment grounding conductor size to
address voltage drop considerations shall not be required.)
Joel Davidson wrote:
>
> You will get better lightning protection if you connect the array and
> house
> panel and any other grounds together and also put a ground rod on the
> same
> grounding conductor at the array to minimize the potential between the
> array
> and the house panel. The mindset to have is all electrical and chassis
> grounds should have the same minimum resistance and all ground tied
> together. Copper conductors and ground rounds are still the lowest cost
> and
> best lightning and grounding protection.
>
> ----- Original Message -----
> From: "Ray Walters" <walters at taosnet.com>
> To: <RE-wrenches at topica.com>
> Sent: Sunday, June 29, 2008 3:18 PM
> Subject: Re: 350 feet to barn- grounding [RE-wrenches]
>
>
> >
> > Steve;
> >
> > For lightning protection purposes, you're right. It would be better to
> > not connect the grounding systems. For grouchy inspectors though, I
> > think
> > you'll need that ground wire. You may be able to run a bare copper
> > conductor outside the conduit, which would help reduce your impedance
> > to
> > ground.
> > If it helps....Article 690 is more confusing than ever regarding ground
> >
> > requirements. Get the 2008 NEC Handbook with illustrations, and try to
> > make sense out of it all: you and the inspector will be crying in no
> > time....
> > Have some tissues and donuts on hand, and he may just walk away without
> >
> > giving you a hard time.
> >
> > Ray Walters
> >
> >
> > On Jun 29, 2008, at 3:34 PM, Steve Johnson wrote:
> >
> >>
> >> I have a grid tied installation where the panels are 350 ft. from the
> >> inverter. This is not a voltage drop problem because I have 370 Vmp DC
> >> to work with so wire is sized < 1% Vd.
> >>
> >> Is there any reason to run a ground wire from the barn to the house in
> >> the underground conduit? I can't think of one. The 4 strings on the
> >> barn will be combined at the barn, with a lightning arrestor and ground
> >> rod installed.
> >>
> >> At the house the DC disconnect will be grounded on the AC and DC side.
> >> This seems fine to me but there is a gnawing subconcious feeling that
> >> makes me ask this question. Or maybe its the grouchy inspector.
> >>
> >> Steve
> >>
> >>
> >>
> >
> >
> > - - - -
> > Hosted by Home Power magazine
> >
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages:
> > http://lists.topica.com/lists/RE-wrenches/read
> >
> > List rules & how to change your email address:
> > www.mrsharkey.com/wrenches/etiquette.php
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/
> >
> > Moderator: michael.welch at homepower.com
> >
>
Steve Johnson
LightWave Solar Electric
Nashville, Tennessee
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list