350 feet to barn- grounding [RE-wrenches]
Joel Davidson
joel.davidson at sbcglobal.net
Sun Jun 29 16:34:20 PDT 2008
<x-flowed>
You will get better lightning protection if you connect the array and house
panel and any other grounds together and also put a ground rod on the same
grounding conductor at the array to minimize the potential between the array
and the house panel. The mindset to have is all electrical and chassis
grounds should have the same minimum resistance and all ground tied
together. Copper conductors and ground rounds are still the lowest cost and
best lightning and grounding protection.
----- Original Message -----
From: "Ray Walters" <walters at taosnet.com>
To: <RE-wrenches at topica.com>
Sent: Sunday, June 29, 2008 3:18 PM
Subject: Re: 350 feet to barn- grounding [RE-wrenches]
>
> Steve;
>
> For lightning protection purposes, you're right. It would be better to
> not connect the grounding systems. For grouchy inspectors though, I think
> you'll need that ground wire. You may be able to run a bare copper
> conductor outside the conduit, which would help reduce your impedance to
> ground.
> If it helps....Article 690 is more confusing than ever regarding ground
> requirements. Get the 2008 NEC Handbook with illustrations, and try to
> make sense out of it all: you and the inspector will be crying in no
> time....
> Have some tissues and donuts on hand, and he may just walk away without
> giving you a hard time.
>
> Ray Walters
>
>
> On Jun 29, 2008, at 3:34 PM, Steve Johnson wrote:
>
>>
>> I have a grid tied installation where the panels are 350 ft. from the
>> inverter. This is not a voltage drop problem because I have 370 Vmp DC
>> to work with so wire is sized < 1% Vd.
>>
>> Is there any reason to run a ground wire from the barn to the house in
>> the underground conduit? I can't think of one. The 4 strings on the
>> barn will be combined at the barn, with a lightning arrestor and ground
>> rod installed.
>>
>> At the house the DC disconnect will be grounded on the AC and DC side.
>> This seems fine to me but there is a gnawing subconcious feeling that
>> makes me ask this question. Or maybe its the grouchy inspector.
>>
>> Steve
>>
>>
>>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list