And that GEC/GE must then also be bonded to the existing premise grounding
system.
 
Mark Frye
Berkeley Solar Electric Systems
271 Vistamont Dr
Grass Valley CA 95945
(530) 401-8024
www.berkeleysolar.com 

-----Original Message-----
From: Mark Frye [mailto:markf at berkeleysolar.com] 
Sent: Friday, June 13, 2008 10:14 AM
To: RE-wrenches at topica.com
Subject: RE: 690.47 (was Enphase) [RE-wrenches]


Drake,

Yes, it really is up in the air, and I am seeing it along different lines.

Most roofs are much more than 6 feet of an electrode.

The intent may have been that you take the most direct route from the array,
down along the side of the building to the ground and put your "additional
electrode" there.  If that is within six feet of the existing premise
electrode, then don't put in the additional electrode.

In any case, you have to run an additional GEC (separate from the DC system
GEC/EGC run as a single conductor from the inverter) from the array to this
new GE.
 
Mark Frye
Berkeley Solar Electric Systems
271 Vistamont Dr
Grass Valley CA 95945
(530) 401-8024
www.berkeleysolar.com 


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list