From: Bill Brooks [mailto:billbrooks7 at yahoo.com] 
Sent: Monday, May 05, 2008 12:27 PM
To: RE-wrenches at topica.com
Subject: RE: point of connection [RE-wrenches]

${top_text_ad}
Dick,

After reading through Article 230 again, I think I agree with your
assessment that there is a single service and multiple service disconnects
when we connect to the supply side of the service disconnect. I also agree
with your assessment that Article 230 is referring to a total service
capacity and does not limit the minimum of individual service connections. 

Article 230 also uses the term "tap", but this is confusing and potentially
dangerous. The "tap rule", commonly referred to in Article 240 only applies
to circuits downstream of the service disconnect and overcurrent protection.

I'm constantly learning and appreciate your insight into the NEC. There is
so much to know and understand about the code, and I want to make sure the
aspects of the code that affect PV systems are understood by myself first
and by those I teach. I will make a point to correct my reference to line
side service connections (and still avoid the confusing term "tap").

If there is any way you can find the time and finances to make it to our
June 5-6 meeting in Golden, Colorado, we could certainly use your input.
Please contact me offline to discuss your involvement at 707-332-0761.

Bill.


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list