point of connection [RE-wrenches]

Larry Brown, Sunmountain sunmountain at netstep.net
Sat May 3 08:08:24 PDT 2008


<x-flowed>

David,

The DC STC input  is 4800 watts on each inverter

Larry


On May 3, 2008, at 9:31 AM, David Buckner wrote:

>
> Wrenches,
> If Larry's line side service connection, even with its closer  
> proximity, becomes costlier than the potential load side  
> connection, could he feed a subpanel with the two 30A PV input  
> breakers, then feed into the house MDP with a 40A breaker from this  
> subpanel?  This would require calculations of DC input and  
> resulting max AC output of the inverters.  If the inverters  won't  
> ever be putting out 20A anyway, then the 40A (continuous duty?)  
> breaker shouldn't be tripping and code would be met?  I'm asking,  
> not telling.  Larry, what is the DC STC input anyway?
>
> David
>
>
> -----Original Message-----
> From: Larry Brown, Sunmountain <sunmountain at netstep.net>
> Sent: Friday, May 02, 2008 1:09 PM
> To: RE-wrenches at topica.com <RE-wrenches at topica.com>
> Subject: point of connection [RE-wrenches]
>
>
> Wrenches,
>
> We are doing an installation with 2 Sunny Boy 5000 inverters each
> requiring a 30 amp 2 pole breaker.  The closest point of
> interconnection is outside the house on the supply side of the main
> service disconnect near the customer side of the utility meter.
> According to 690.64B on the load side we are limited to 120% of the
> busbar rating, which means we could not put 2- 30 amp backfeed
> breakers in the main 200 amp service panel.  But 690.64A does not
> state a limitation  of 120% .  So we are considering a 200 amp feed
> through panel, also recommended by our local electrical inspector,
> and then putting our 2-30 amp 2 pole breakers in this feed thru
> panel. Anyone have any comments on this method? What other methods
> are people using to make a supply side interconnection?
>
> Larry Brown
> Sun Mountain
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE- 
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/ 
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE- 
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/ 
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
>


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>



More information about the RE-wrenches mailing list