[RE Marketing] 400 ft DC voltage drop [RE-wrenches]
Ray Walters
walters at taosnet.com
Thu May 1 14:27:59 PDT 2008
<x-flowed>
My spread sheet sizer uses the NEC formulas and uses their temp.
corrections as well. You can input both ambient and conductor temps.
Contact me off list if you want a copy.
ray at solarray.com
On May 1, 2008, at 7:41 AM, Tom DeBates wrote:
>
> good day Wrenches,
> I have used NEC Chapter 9, Table 8 for DC conductor resistance and
> have noticed that the data is for conductors @ 75C. Since most of
> these
> "runs" would be below grade, wouldn't the conductor temp be lower
> (~20C
> ?) I see that Note #2 has a correction factor, but I've always been
> too
> lazy to try it. Has anyone done this and, if so, has it made much of a
> difference?
> thanks,
> Tom
> Jeff Clearwater, Village Power Design wrote:
>>
>> Hi Steve,
>>
>> William' approach is exactly it. We use to do 1% at Vmp but as
>> copper prices increased we did a more careful analysis of the peak vs
>> average issue and now use 1.5% But as he says make sure that's from
>> panel to inverter, not just from combiner to disconnect. I do take a
>> look at Vmin (the inverter's MPPT min) for the worst case scenario
>> but that usually doesn't go over 2% if Vmp is at 1.5% or better.
>>
>> That said if the run is short or the pull easy I tend to bump up a
>> size to maximize those precious PV watts which usually puts me back
>> in the 1% range at Vmp - but if the run is long and the cost starts
>> going up - William's perspective is what we use.
>>
>> Hope that helps!
>>
>> Jeff Clearwater
>> Village Power Design
>>
>>
>>> Steve:
>>>
>>> I'd say E because high temp Emp will occur at lower output amperage.
>>> I doubt the difference between D or E will be significant and Voc
>>> does not count.
>>>
>>> Consider this concept: Rated current occurs rarely, if ever.
>>> Assume, though, it occurs at noon. The rest of the day presents
>>> varying degrees of lesser current. What is the area under the
>>> curve? My research indicates it is 50% of the peak amperage.
>>>
>>> What does this mean? It means that if you design a PV feeder for 2%
>>> voltage drop at peak output, it will average 1% over the day. Or,
>>> design criteria for PV feeders is only half as important as we think
>>> it is. (Don't forget to quantify cumulative loses throughout all
>>> feeders and components, however.)
>>>
>>> William Miller
>>>
>>>
>>> At 10:18 PM 4/30/2008, you wrote:
>>>> I have a 400 foot run on an output circuit to combiner, 23.5 amps.
>>>> Should the DC VOLTAGE that is used as the system voltage to
>>>> calculate
>>>> voltage drop be:
>>>> A) Voc at low temperature
>>>> B) Voc at high temperature
>>>> C) Nameplate Voc
>>>> D) Vmp at high Temperature
>>>> E) Nameplate Vmp
>>>>
>>>
>>
>>
>> --
>> ~~~~~~~~~~~~~
>> Jeff Clearwater
>> Village Power Design
>> Sustainable Energy & Water Solutions for Home & Village
>> http://www.villagepower.com
>> gosolar at villagepower.com
>> NABCEP (tm) Certified Solar PV Installer
>>
>> Voice: 413-259-3776
>> Fax: 413-825-0703
>> 65 Schoolhouse Rd
>> Amherst, MA 01002
>> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
R. Walters
Solarray.com
NABCEP # 04170442
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list