Hi William;
I noticed that change in the series fuse rating about the time they
changed to the MC connectors and changed the module dimensions
slightly too. I caught it last summer? But I had thought about three
strings with the old numbers too.
Ray
On Feb 26, 2008, at 5:59 PM, William Miller wrote:
>
> Ray, Colleagues:
>
> I have been scratching my head ever since Ray sent me the e-mail
> below. I was very certain that at one point in time I had been
> convinced by a Fronius engineer that 3 strings of Solar World
> modules are allowed without fusing. When Ray sent this e-mail,
> rechecked my calculations and found that they do not work.
>
> Just now I realized that Solar World changed the specified series
> fuse ratings sometime in the recent past. In 2006 and before, the
> SW175 had a series fuse rating of 20 amps, which allowed the three
> strings ((3-1)*5.3*1.56<20). I actually found a photo of a module
> label if anyone really needs documentation on this.
>
> The series fuse rating now is 15 amps and three strings are not
> allowed. Two strings are allowed.
>
> I apologize, Ray, for leaving this hanging. My memory is not what
> it used to be.
>
> William
>
>
>
> At 11:11 AM 2/8/2008, you wrote:
>
>
>> Well we do have some discrepancies here. William was saying we could
>> go to 3 parallel Solar World strings, John Berdner here says only
>> one, and I'm still saying 2 is good.
>> John I have 2 issues with your excellent analysis.
>> 1) 690.8 B) (1) exception: "Circuits containing an assembly, together
>> with its overcurrent device(s), that is listed for continuous
>> operation at 100% of its rating shall be permitted to be utilized at
>> 100% of its rating."
>> This means that with the right breaker, we don't have to use the 1.56
>> multiplier for array current, only 1.25 which is for edge of cloud
>> effect, etc. I have seen Solar world modules exceed their nameplate
>> rating, so this multiplier is appropriate.
>> 2 x 5.1 A x 1.25 = 12.75 Amps on a 15A breaker that is rated for 100%
>> duty is acceptable. (most Outback and Midnite solar offerings are
>> 100% rated BTW)
>>
>>
>> R. Walters
>> Solarray.com
>> NABCEP # 04170442
>
>
>
> --
> This message has been scanned for viruses and
> dangerous content by MailScanner, and is
> believed to be clean.
>
>
> This e-mail has been scanned for SPAM and virus infections using
> Barracuda.
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
R. Walters
Solarray.com
NABCEP # 04170442
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list