Multiple Mates, Not that kind. OB Mates! [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Tue Feb 19 14:25:07 PST 2008
Tump -
(Michael - I'll even try to give this answer without any sophomoric
humor)
There still is no multiple MATE solution for the OutBack Power
communication system - unfortunately, only one MATE can still be used on
a system.
The solution I have used on this is to have two MATEs - one in the kiosk
and one in the equipment room - and to just unplug one and connect the
other when required. The OutBack system tolerates hot swapping of MATEs
with only some slight oddities occurring while the old MATE is
disconnected until the new MATE "polls" the system and starts doing the
fine coordination functions
The other option which has also been done is to use a PC based
monitoring system for the kiosk (WinVerter or WattPlot) and keep the
MATE in the equipment room with the computer. Here is a link to our
forum section on the available PC programs which work with the OutBack
system:
Winverter -
http://www.outbackpower.com/forum/viewforum.php?f=30&sid=6d472db9f504640
9da91f849034925f3
WattPlot -
http://www.outbackpower.com/forum/viewforum.php?f=25&sid=6d472db9f504640
9da91f849034925f3
Christopher
Christopher Freitas
Director of Research of Development
OutBack Power Systems, Inc.
cfreitas at outbackpower.com
Tel 360 435 6030
cell 360 202 4239
19009 62nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com
-----Original Message-----
From: Blair May [mailto:tump at hughes.net]
Sent: Sunday, February 17, 2008 1:17 PM
To: RE-wrenches-topica.com
Subject: Multiple Mates, Not that kind. OB Mates! [RE-wrenches]
Is there a way to have 2 OB mates reading information? I have recently
installed a OB DC Flex Mate at a site that will use the Mate 2 as a
display/Kiosk remotely from the Qstack. I would like to have the
ability to read information while in the mechanical room.Chris et all is
this a possibility? do they IF this can be done need the latest up grade
software EVEN if I have no interest in the information that is being
displayed on the Mate 2/Kiosk?
<mailto:Tump at hughes.net> Tump at hughes.net
<http://www.swnl.net/> www.SWNL.net
Solarwinds Northernlights
Serving Mid Coast Maine & Northern California
Me.# 207-832-7574 Cl.# 610-517-8401
******** MAINE'S CHARTER ********
NABCEP "Certified PV Designer & Installer"
******** MAINE'S CHARTER ********
Trace Xantrex "Certified" Dealer / Installer"
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
EMAIL CONFIDENTIALITY NOTICE:
The preceding message (including attachments) is covered by the Electronic Communication
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by
attorney-client or other privilege. If you believe that it has been sent to you in error,
please do not read it. If you are not the intended recipient,you are hereby notified
that any retention, dissemination, distribution, or copying of this communication is
strictly prohibited. Please reply to the sender that you have received the message in
error, then delete it. Thank you.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list