M-C branch plugs: Legal? Safe? [RE-wrenches]
Ray Walters
walters at taosnet.com
Mon Feb 4 10:07:57 PST 2008
<x-flowed>
First, you can't use those connectors to create more than 2 parallel
strings, so I'm not sure how you would parallel 3 strings. (unless
you doubled them up?)
2nd, we never exceed the fuse string series rating. We use Solar
World 165s: the series fuse rating is 15 amps, and we have 2 modules
with a Asc of 5.5, then we have 11 A of current x 1.25 = 13.75 A,
which is under the 15 A breaker we will use to protect this
paralleled sub array. We are using a 100% duty rated breaker, so we
don't need to use the full 1.56 multiplier.
We have actually seen damage many times from over paralleled arrays.
The connectors themselves (inside the module j-boxes) have melted
from the heat from a slightly loose connection.
30 amps all day every day x some slight resistance can equal enough
heat to do damage.
I wouldn't exceed the fuse rating of the module, End of Story. I can
create some nightmares using all UL listed equipment. Just because it
goes together doesn't make it right.
Ray Walters
On Feb 4, 2008, at 8:50 AM, Mick Abraham wrote:
>
> Hi, Wrenchers~
>
> The Multi-Contact "branch connectors" connect two PV strings in
> parallel
> by just plugging them together. MC part numbers for these "branch
> plugs"
> would include PV-AZS3 & PV-AZB3.
>
> These connectors have a UL recognition mark, but they seem non-code
> because there's no individual fusing for each string of modules.
>
> Are code issues raised by this product? I'm working on something where
> there are no codes, so my other question is: are safety issues raised?
>
> Specifically, if one plug-parallels three Kyocera 135's (with, say,
> one
> 30 amp breaker to protect the trio from the 12v battery side), is that
> hazardous? 30 amps exceeds the series fuse rating recommended for the
> KC-135 which again seems non-code. On the other hand, if one uses 10
> gauge plug leads (which are likely fine with 30 amp protection),
> perhaps
> the worries are small.
>
> Multi-Contact rates the branch plugs for 30 amps when 10 gauge wire is
> used. If they're non-code, however, who uses them, and how?
>
> Thanks all around,
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
R. Walters
Solarray.com
NABCEP # 04170442
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list