Mick / Wrenches:
The UL module guys once explained the fuse / no fuse issue in a way
thet really helped me.
Think of the string of modules as a piece of wire with an ampacity that
is set by the UL series fuse rating.
If you then fault that "wire" then there will be current flow from the
other strings wired in parallel with it.
You can then calculate the fault current at 1.25 Isc of the other
parallel strings.
If the result is more than the UL series fuse rating of the module then
you have a design problem (regardless of the wire size feeding the
strings).
If it is a Code issue or not is still an open question since the Code
does not really address the issue of UL series fuse size being used as
an ampacity.
Logically this interpretation makes sense but the Code does not
specifically address the issue of module "ampacity".
Best Regards,
John Berdner
>>> mick at abrahamsolar.com 2/4/2008 07:50:42 AM >>>
Hi, Wrenchers~
The Multi-Contact "branch connectors" connect two PV strings in
parallel
by just plugging them together. MC part numbers for these "branch
plugs"
would include PV-AZS3 & PV-AZB3.
These connectors have a UL recognition mark, but they seem non-code
because there's no individual fusing for each string of modules.
Are code issues raised by this product? I'm working on something where
there are no codes, so my other question is: are safety issues raised?
Specifically, if one plug-parallels three Kyocera 135's (with, say, one
30 amp breaker to protect the trio from the 12v battery side), is that
hazardous? 30 amps exceeds the series fuse rating recommended for the
KC-135 which again seems non-code. On the other hand, if one uses 10
gauge plug leads (which are likely fine with 30 amp protection),
perhaps
the worries are small.
Multi-Contact rates the branch plugs for 30 amps when 10 gauge wire is
used. If they're non-code, however, who uses them, and how?
Thanks all around,
Mick Abraham, Proprietor
www.abrahamsolar.com
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list