Steve:
By AC I assume you mean air conditioning. Air conditioning disconnects are
not allowed to be installed in accessible locations if live parts inside
are accessible. Correct practice is to use "pull-out" disconnects that
have a "dead-front" panel. Below is the pertinent code citation:
110.27 Guarding of Live Parts.
(A) Live Parts Guarded Against Accidental Contact. Except as elsewhere
required or permitted by this Code, live parts of electrical equipment
operating at 50 volts or more shall be guarded against accidental contact
by approved enclosures or by any of the following means:
(1) By location in a room, vault, or similar enclosure that is accessible
only to qualified persons.
(2) By suitable permanent, substantial partitions or screens arranged so
that only qualified persons have access to the space within reach of the
live parts. Any openings in such partitions or screens shall be sized and
located so that persons are not likely to come into accidental contact with
the live parts or to bring conducting objects into contact with them.
(3) By location on a suitable balcony, gallery, or platform elevated and
arranged so as to exclude unqualified persons.
(4) By elevation of 2.5 m (8 ft) or more above the floor or other working
surface.
In the PV industry, we are forced to use industrial disconnects for DC and
sometimes AC (alternating current) circuits. Being industrial equipment,
there are no dead-front panels inside. We deal with this by securing the
covers with wrench tightened bolts and ensure that this practice is
followed through training. Below is a link to our web-base training text.
http://mpandc.com/practices/Procedures/Disconnect_locking/Disconnect_Locking.html
I hope you are not presenting the logic: "well, there are lots of illegal
air conditioning disconnects out there so we don't need to worry about PV
wiring safety..." This would not be a prudent line of deduction.
William Miller
At 08:25 AM 1/24/2008, you wrote:
>Most every house has 240 AC disconnects at kid level that can be fairly
>easily opened and has exposed live metal inside. This hasn't been a
>problem and it is everywhere.
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list