[RE-wrenches] DLO wires in PV systems
    Michael  Cook 
    mike at powerupco.com
       
    Mon Dec  1 13:01:27 PST 2008
    
    
  
The wires are in a Solardock mounting system, so they are not exposed, and
are then run in conduit.  Is the UV exposure rating the only difference?
 
 
 
Mike
 
 
  _____  
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Monday, December 01, 2008 3:51 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] DLO wires in PV systems
 
Mike,
The RHH/RHW-2 do not cross to USE-2 because they do not have any rating for
UV exposure.
 
If these conductors are run outside of conduit on the array, you need USE-2
or PV conductor.
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  
 
 
  _____  
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Michael Cook
Sent: Monday, December 01, 2008 12:47 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] DLO wires in PV systems
We have a 4KW pv system installed and the local inspector wants to use this
as a test case so he is crossing all T's and dotting all I's.  Which I am
happy to help him out with training his other inspectors   We are running
into an issue on the module output wires.  USE-2 or PV rated is how the code
book reads.  The wire we have been using on these systems is DLO (diesel
locomotive) which carries the ratings of RHH and RHW-2, which seems to cross
with the USE-2.  Does anyone have any documentation showing this cross?  If
not, I guess I will be switching the wire to USE-2/RHW-2 because it needs to
go into conduit.
 
 
 
Mike
mike at powerupco.com
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081201/e848cff6/attachment-0003.html>
    
    
More information about the RE-wrenches
mailing list