The RHH/RHW-2 do not cross to USE-2 because they do not have any rating for
UV exposure.
If these conductors are run outside of conduit on the array, you need USE-2
or PV conductor.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Michael Cook
Sent: Monday, December 01, 2008 12:47 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] DLO wires in PV systems
We have a 4KW pv system installed and the local inspector wants to use this
as a test case so he is crossing all T's and dotting all I's. Which I am
happy to help him out with training his other inspectors We are running
into an issue on the module output wires. USE-2 or PV rated is how the code
book reads. The wire we have been using on these systems is DLO (diesel
locomotive) which carries the ratings of RHH and RHW-2, which seems to cross
with the USE-2. Does anyone have any documentation showing this cross? If
not, I guess I will be switching the wire to USE-2/RHW-2 because it needs to
go into conduit.