[RE-wrenches] Request for Enphase inverter comments
Geoff Greenfield
geoff at third-sun.com
Fri Oct 24 10:14:33 PDT 2008
Thanks Marv (and thanks Michael W. for clarification).
Marv - could you comment on the grounding requirements? Am I correct that I can't just daisy chain inverter chassis grounds and land at a sub-panel AC ground bar? (and that this inverter chasis ground is in addition to the DC module frame/rack grounding we are used to?).
For a brighter energy future,
Geoff Greenfield
Chief Executive Officer
Third Sun Solar & Wind Power Ltd.
340 West State Street, Unit 25
Athens, OH 45701
740.597.3111 Fax 740.597.1548
www.Third-Sun.com
Clean Energy - Expertly Installed
----- "Marv Dargatz" <mdargatz at enphaseenergy.com> wrote:
> Wrenches,
>
> The Enphase system meets all regulatory requirements for a utility
> interactive PV system. Also, we were very careful and thorough in
> making sure that it meets all NEC requirements. If you run into an
> AHJ
> who has objections, please put them in contact with our Customer
> Support
> people at (877)797-4743.
>
> Any new technology raises new questions, and there are always some
> doubting Thomas's. We have been dealing with this on a case by case
> basis. Usually it is just a matter of education.
>
> Both Bill Brooks and John Wiles are well aware of our products and
> their
> application in the field. We can certainly ask for their assistance
> in
> addressing AHJ objections.
>
> Regarding disconnects; connectors can serve as disconnects. Also,
> 690.18 specifically allows an opaque covering to disable the module.
> This is especially appropriate with a micro-inverter connected to a
> single module.
>
> Please let me know if I can help.
>
> See Ya!
>
> Marv
> Enphase Energy
> 707 763-4784 x7016
>
> Eric Andrews wrote:
> > Our AHJ has a list of reasons that shoot down even the thought of
> using
> > Enphase... including, his requirement for AC and DC discos on each
> > inverter...
> >
> > Eric R. Andrews
> > NABCEP Certified PV Installer
> > Eco Solar, Inc.
> > Klamath Falls, OR 97601
> >
> >
> >
> > Hi Gang,
> >
> > For the number of ads I've seen for the product, I am surprised that
> there
> > has been no discussion of the benefits/disadvantages of this micro
> inverter
> > product.
> >
> > TIA,
> > Bill Loesch
> > Solar 1 - Saint Louis Solar
> > 314 631 1094
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> >
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> >
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
> >
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
More information about the RE-wrenches
mailing list