Questions for Enphase Reps [RE-wrenches]
Bill Brooks
billbrooks7 at yahoo.com
Thu Jun 12 22:00:07 PDT 2008
The 2008 NEC allows sizing of combined GEC and EGC to be same size as EGC in
690.47(C) in an inverter with GFP. Whether it should be allowed or not is
another issue. In California, using the 2005 NEC, 8AWG is the smallest GEC
allowed.
Bill.
-----Original Message-----
From: Drake Chamberlin [mailto:Drake.Chamberlin at redwoodalliance.org]
Sent: Thursday, June 12, 2008 9:10 PM
To: RE-wrenches at topica.com
Subject: RE: Questions for Enphase Reps [RE-wrenches]
Hello Bill,
At 06:27 PM 6/12/2008, you wrote:
>Depending on the version of the NEC your are using, it is possible to have
a
>combined dc GEC and ac EGC that is as small as 14 AWG
I'm glad to get your confirmation about this. Although this seems
to be accepted by our inspectors, I'm not sure why we are allowed to
have an GEC smaller than #8. How does that work?
Thanks,
Drake
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list