grid-tie inverters & generators [RE-wrenches]
daryl_solar at yahoo.com
daryl_solar at yahoo.com
Thu Jun 5 05:15:46 PDT 2008
I have done several AC coupled systems using Outback and PVPowered, with very good luck, I use the critical circuit approach and the ATS is in the Outback. HOwever I am limited in power with the present Outback configuratuin, and Outback is close to a change that makes this limit larger. On small genny systems I have had good luck with DC coupled.
If the CC load is to large for the inverter to handle, a genny support inverter (Xantrex XW) the CC load. I have done some genny support with Outback, but have been told this is not an approved approach.
I look forward to more information and perhaps I have an oddball data I can add. contact off list if you want.
DT
--- On Wed, 6/4/08, Kurt Albershardt <info at es-ee.com> wrote:
> From: Kurt Albershardt <info at es-ee.com>
> Subject: RE: grid-tie inverters & generators [RE-wrenches]
> To: RE-wrenches at topica.com
> Date: Wednesday, June 4, 2008, 11:00 AM
> Critical circuits would be ideal, but the design gets
> complicated quickly when you try to accommodate utility
> interconnection requirements. If I backfeed the critical
> circuits panel and put an ATS or MTS ahead of that, when
> the genset fires up the UL1741 inverter should ideally sync
> to (and reduce the load on) the genny.
>
> Would love a safe, reliable way to do this without a genny,
> providing daytime power to run a few critical loads. If I
> could wake up something like a small Exeltech would the big
> inverters sync to it? Would the Exeltech overload and drop
> out before the load could be shared, or would I need
> coordinated switchgear to manage the changeover?
>
>
>
>
> --On Wednesday, June 04, 2008 6:35 AM -0700
> daryl_solar at yahoo.com wrote:
>
> >
> > I have tried something like this, not with SMA
> however. to determine if my experiance is relevent, what
> is the max load to be served? Is this a critical curcits
> situatuion, or total load? Are batteries to be part of
> the picture?
> > Darryl
> >
> >
> > --- On Tue, 6/3/08, Kurt Albershardt
> <info at es-ee.com> wrote:
> >
> >> From: Kurt Albershardt <info at es-ee.com>
> >> Subject: RE: grid-tie inverters & generators
> [RE-wrenches]
> >> To: RE-wrenches at topica.com
> >> Date: Tuesday, June 3, 2008, 6:00 PM
> >>
> >> I am interested in what others have learned about
> grid tie
> >> and engine-generators. Seems silly to idle all
> that
> >> expensive PV just because the utility has a bad
> day or
> >> three...
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list