Outback MX problem [RE-wrenches]
Larry Crutcher, Starlight Solar
larry at starlightsolar.com
Wed May 28 15:11:26 PDT 2008
<x-flowed>
Ron,
If you are saying you measured the voltage at the MX terminals and had a 4
volt difference between your meter and the MX display, I would send the MX
back for replacement.
If you are saying the 4 volt drop was between the battery terminals (your
meter) and the MX display while charging, there might be a bad connection
somewhere from the MX to the battery. Is this a new installation or just a
new problem?
A bad connection will cause the MX will reach the absorb set point quickly
due to resistance and then switch to float unless you set the minimum absorb
timer (advanced menu: Absorb Time Limits).
Matt, after sitting through a couple Surrette training sessions, I was
thinking he has the absorb voltage a little low. I'm a big fan of
aggressive, temperature compensated, charge voltage for daily deep cycle
applications. 2.47vpc is what I use for flooded cells. 29.4 is spot on
according to Rolls Bulletin 605. What do you use for absorb voltage?
Larry Crutcher
Starlight Solar
powered by STARLIGHT(tm)
----- Original Message -----
From: Matt Tritt
To: RE-wrenches at topica.com
Sent: Wednesday, May 28, 2008 12:42 PM
Subject: Re: Outback MX problem [RE-wrenches]
Ron,
Since the MX thinks that the batteries are virtually full all the time,
"force bulk" is simply overriding the controller programming to effect a
charge, I would take OutBack up on the offer and call it good. I'm
curious as to why you have the bulk point set so high?
Matt T
Ron Young wrote:
>
> I'm having a problem with an Outback MX going into sleep mode and showing
> incorrect voltage on the input. It's a single 3524 inverter with a 4KS25
> Surrette battery charged by a Whisper 100 and a 680 watt array (Evergreen
> 170's) wired in two strings for 48v. The only time the MX will charge is
> if a charge is initiated via FORCE BULK mode or if the customer turns on
> her vacuum cleaner and it draws down the batt. voltage then the MX kicks
> in. She says she sees the pv output voltage drop from 70 (sunny day) to
> as low as 24 then start building up again. If it stays around 60 then the
> MX keeps charging but once it gets back up to 70 then MX cuts out. Bulk
> set point is at 29.4.
>
> Actual battery voltage measured at the terminals is 25.1 today but the MX
> says 29.1.
>
> Outback wants to replace the unit but I'm not convinced yet that it's
> defective, just wondering if maybe something else is going on that I've
> overlooked. The above behaviour is the same whether there is wind or no
> wind so I've ruled out a conflict with the Whisper controller.
>
> Ron Young
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--
No virus found in this incoming message.
Checked by AVG.
Version: 7.5.524 / Virus Database: 269.24.1/1470 - Release Date: 5/28/2008
7:20 AM
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list