good day Wrenches,
I have used NEC Chapter 9, Table 8 for DC conductor resistance and
have noticed that the data is for conductors @ 75C. Since most of these
"runs" would be below grade, wouldn't the conductor temp be lower (~20C
?) I see that Note #2 has a correction factor, but I've always been too
lazy to try it. Has anyone done this and, if so, has it made much of a
difference?
thanks,
Tom
Jeff Clearwater, Village Power Design wrote:
>
> Hi Steve,
>
> William' approach is exactly it. We use to do 1% at Vmp but as
> copper prices increased we did a more careful analysis of the peak vs
> average issue and now use 1.5% But as he says make sure that's from
> panel to inverter, not just from combiner to disconnect. I do take a
> look at Vmin (the inverter's MPPT min) for the worst case scenario
> but that usually doesn't go over 2% if Vmp is at 1.5% or better.
>
> That said if the run is short or the pull easy I tend to bump up a
> size to maximize those precious PV watts which usually puts me back
> in the 1% range at Vmp - but if the run is long and the cost starts
> going up - William's perspective is what we use.
>
> Hope that helps!
>
> Jeff Clearwater
> Village Power Design
>
>
> >Steve:
> >
> >I'd say E because high temp Emp will occur at lower output amperage.
> >I doubt the difference between D or E will be significant and Voc
> >does not count.
> >
> >Consider this concept: Rated current occurs rarely, if ever.
> >Assume, though, it occurs at noon. The rest of the day presents
> >varying degrees of lesser current. What is the area under the
> >curve? My research indicates it is 50% of the peak amperage.
> >
> >What does this mean? It means that if you design a PV feeder for 2%
> >voltage drop at peak output, it will average 1% over the day. Or,
> >design criteria for PV feeders is only half as important as we think
> >it is. (Don't forget to quantify cumulative loses throughout all
> >feeders and components, however.)
> >
> >William Miller
> >
> >
> >At 10:18 PM 4/30/2008, you wrote:
> >>I have a 400 foot run on an output circuit to combiner, 23.5 amps.
> >>Should the DC VOLTAGE that is used as the system voltage to calculate
> >>voltage drop be:
> >>A) Voc at low temperature
> >>B) Voc at high temperature
> >>C) Nameplate Voc
> >>D) Vmp at high Temperature
> >>E) Nameplate Vmp
> >>
> >
>
>
> --
> ~~~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> Sustainable Energy & Water Solutions for Home & Village
> http://www.villagepower.com
> gosolar at villagepower.com
> NABCEP (tm) Certified Solar PV Installer
>
> Voice: 413-259-3776
> Fax: 413-825-0703
> 65 Schoolhouse Rd
> Amherst, MA 01002
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list