Direct Grid Tie Ground Wire [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Mon Apr 7 16:17:42 PDT 2008
Drake,
I read it as you read, it is both and it does have to be #8. We are lucky
that they are allowing it to be the same conductor. However, unless you can
get your AHJ to let you drop the #8 requirement on the DC ground electrode
conductor (or system ground)(seems reasonable to me for small sized systems)
then the 10/3 with ground won't cut it.
Either run the separate #8 GEC or run 8/3 with ground, or run flex and pull
#10's and the #8. I prefer the to run the flex and pull.
:-(
Mark Frye
Berkeley Solar Electric Systems
271 Vistamont Dr
Grass Valley CA 95945
(530) 401-8024
www.berkeleysolar.com
-----Original Message-----
From: Drake Chamberlin [mailto:Drake.Chamberlin at redwoodalliance.org]
Sent: Monday, April 07, 2008 6:04 PM
To: RE-wrenches at topica.com
Subject: Direct Grid Tie Ground Wire [RE-wrenches]
Hello Wrenches,
I've been reading the 2008 code and talking to an inspector who is
studying 690 very thoroughly. A question arises about the grounding
conductor between the AC service panel and the inverter. Is it an
equipment grounding conductor or a grounding electrode conductor, or both?
It would need to be both if there were both AC and DC systems. This
is covered in 690.47(C), "Systems with Alternating-Current and
Direct-Current Grounding Requirements." Unless the array had plastic
frames, it would seem that there would always be DC grounding
requirements, so what does this mean?
This is direct grid tie with no DC loads. It seems another section
would need to be added to deal with a direct grid tie system.
The main issue that arises from this is that if the ground wire is
considered a grounding electrode conductor, it needs to be #8. This
would mean that a 10/3 WG cable would need to have a separate ground
wire run that is at least #8. It would probably be easier to run a
#6 since it can be run of the surface.
How have you and your inspectors been interpreting this?
Thanks,
Drake
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list