Evaluation of XW charge control [RE-wrenches]
William Miller
wrmiller at charter.net
Fri Feb 22 13:17:16 PST 2008
<x-flowed>
Kirpal:
Thanks for your comments. This reminds me of a potential design defect of
the XW charge controller: The manual indicates that you must put the unit
in standby before disconnecting the unit or damage could result. If indeed
failure to activate standby mode on disconnect will damage the unit, we
consider this a design flaw. It is likely that untrained customers will
fail to navigate to the standby mode and instead just activate the circuit
breaker disconnect.
To prevent this, we are installing these controllers with two pole
breakers-- one pole for input and one for output. With this configuration,
the unit is entirely disconnected with one action, hopefully preventing damage.
William Miller
At 12:56 PM 2/22/2008, you wrote:
>Wiliam....one other advantage is the integrated ground fault
>protection.......makes for cheaper and quicker
>installation....especially as all PV systems will be required to have
>GFP included.....keep us posted.....we still have not done any XW
>systems......waiting for more feed back so i appreciate yours......
>
>Sunny REgards,
>Kirpal
>Renewable Energy Systems
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list